In this situation, I am working on a small maintenance building, which would 
not be required to be sprinklered per IBC. The Engineer wants to install 
sprinklers below the ceiling, but not in a combustible attic. My stamping hand 
is twitching a little.


At 04:28 PM 8/11/2011, you wrote:
>But let's say the applicable code is IBC which allows a partial system and
>requires 13 for the installation requirements.. Can he then install the
>partial system or does the rule in 13 requiring sprinklers throughout trump
>the IBC allowance of partial protection?
>
>On Thu, Aug 11, 2011 at 1:20 PM, <[email protected]> wrote:
>
>> A prime example of this would be an office building that by code doesn't
>> require sprinklers but the owner decides to install them anyway.  If he does
>> then the installation must conform to the applicable Code and Standard.
>>
>> This is not really that complicated.
>>
>>
>> Craig L. Prahl, CET
>> Fire Protection
>> CH2MHILL
>> Lockwood Greene
>> 1500 International Drive
>> Spartanburg, SC  29304-0491
>> Direct - 864.599.4102
>> Fax - 864.599.8439
>> CH2MHILL Extension  74102
>> [email protected]
>>
>>
>>
>> -----Original Message-----
>> From: [email protected] [mailto:
>> [email protected]] On Behalf Of Todd Williams
>> Sent: Thursday, August 11, 2011 3:04 PM
>> To: [email protected]
>> Subject: non-required systems
>>
>> The exception in section 901.2 of the IBC (2003) states: "Exception: Any
>> fire protection system or portion thereof not required by this code shall be
>> permitted to be installed for partial or complete protection provided that
>> such system meets the requirements of this code."  Does this mean that an
>> Architect/Owner can pick and chose what the wants to protect if the system
>> is not required? Anybody dealt with this from a liability standpoint?
>>
>> Todd G. Williams, PE
>> Fire Protection Design/Consulting
>> Stonington, CT
>> 860.535.2080
>> www.fpdc.com
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>
>
>
>-- 
>Ron Greenman
>Instructor
>Fire Protection Engineering Technology
>Bates Technical College
>1101 So. Yakima Ave.
>Tacoma, WA 98405
>
>[email protected]
>
>http://www.bates.ctc.edu/fireprotection/
>
>253.680.7346
>253.576.9700 (cell)
>
>Member:
>ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC
>
>They are happy men whose natures sort with their vocations. -Francis Bacon,
>essayist, philosopher, and statesman (1561-1626)
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to