Trumping and Enforcement.................

Emphasis in CAPS

2009 IBC (Model Code)

102.4 Referenced codes and standards. The codes and standards referenced in
this code SHALL BE CONSIDERED PART OF THE REQUIREMENTS OF THIS CODE to the
prescribed extent of each such reference. Where differences occur between
provisions of this code and referenced codes and standards, the provisions
of this code shall apply.


N.J.A.C. 5:23-3.14     Building subcode  (New Jersey)
  
(a) Rules concerning the building subcode are as follows:
  
1. Pursuant to authority of P.L. 1975, c. 217, as modified by P.L. 1996, c.
53, the Commissioner hereby adopts the model code of the International Code
Council, 2009 International Building Code, known as the "IBC/2009." This
code is hereby adopted by reference as the building subcode for New Jersey
subject to the modifications stated in (b) below.
  
i. Copies of this code may be obtained from the International Code Council
at 4051 West Flossmoor Road, Country Club Hills, Illinois 60478-5795.
ii. The IBC/2009, as amended, may be known and cited as the "building
subcode."

1. Chapter 1, Scope and Administration, shall be deleted in its entirety. In
addition, any referenced section of Chapter 1 shall be deleted throughout
the code and "the administrative provisions of the Uniform Construction Code
(N.J.A.C. 5:23)" shall be inserted. 

Hope this helps.


John Drucker, CET
Fire Protection Subcode Official 
Fire/Building/Electrical Inspector
Fire Marshals Office
Borough of Red Bank, NJ

Not the official position of any agency, association, committee or
otherwise.  Obtain required applications, permits, inspections and approvals
from Authority(s) Having Jurisdiction. 


 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Todd Williams
Sent: Thursday, August 11, 2011 7:28 PM
To: [email protected]
Subject: Re: non-required systems

A Code has enforcement; a standard does not. 


At 07:16 PM 8/11/2011, you wrote:
>A little aside relative to something Craig said. I think "code trumps
>standard" is a misnomer when the code references the standard as applicable
>as the IBC does in 903.??? relative to 13. 13 then becomes a part of the
>code by reference. I also think that if IBC says you can do something
(i.e.:
>have a partial system in a building that would otherwise not require
>sprinklers) then THAT trumps a sub-paragraph in a portion of code (903.???)
>that would only be applicable in full if the building were required to be
>sprinklered. I think John's passage from the commentary pretty much
supports
>that interpretation. I'd still be leery and keep that passage handy (like
in
>the contract documents) against future possibilities.
>
>On Thu, Aug 11, 2011 at 2:38 PM, John Drucker
<[email protected]>wrote:
>
>> From the 2009 IBC Commentary, Section 901.2;
>>
>> "For example, if a building owner chooses to provide sprinkler protection
>> in
>> a certain area and such protection is not required by the code, the
system
>> MUST BE INSTALLED IN ACCORDANCE WITH THE APPLICABLE NFPA STANDARD and
other
>> APPLICABLE requirements of the code such as water supply and supervision.
>> The EXTENT of the protection would not be regulated".
>>
>> So the stakeholder defines the extent of the protected area, the
protection
>> within that area, the water supply, supervision and other features that
>> serve that area must comply with the standard. When dealing with "not
>> required" applications a performance statement indicating the fire
>> protection goals of the intended protection is in order. The goals must
>> match the design.
>>
>> Hope that helps.
>>
>>
>> John Drucker, CET
>> Fire Protection Subcode Official
>> Fire/Building/Electrical Inspector
>> Fire Marshals Office
>> Borough of Red Bank, NJ
>>
>> Not the official position of any agency, association, committee or
>> otherwise.  Obtain required applications, permits, inspections and
>> approvals
>> from Authority(s) Having Jurisdiction.
>>
>>
>>
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of Todd
>> Williams
>> Sent: Thursday, August 11, 2011 3:04 PM
>> To: [email protected]
>> Subject: non-required systems
>>
>> The exception in section 901.2 of the IBC (2003) states: "Exception: Any
>> fire protection system or portion thereof not required by this code shall
>> be
>> permitted to be installed for partial or complete protection provided
that
>> such system meets the requirements of this code."  Does this mean that an
>> Architect/Owner can pick and chose what the wants to protect if the
system
>> is not required? Anybody dealt with this from a liability standpoint?
>>
>> Todd G. Williams, PE
>> Fire Protection Design/Consulting
>> Stonington, CT
>> 860.535.2080
>> www.fpdc.com
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>
>
>
>-- 
>Ron Greenman
>Instructor
>Fire Protection Engineering Technology
>Bates Technical College
>1101 So. Yakima Ave.
>Tacoma, WA 98405
>
>[email protected]
>
>http://www.bates.ctc.edu/fireprotection/
>
>253.680.7346
>253.576.9700 (cell)
>
>Member:
>ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC
>
>They are happy men whose natures sort with their vocations. -Francis Bacon,
>essayist, philosopher, and statesman (1561-1626)
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to