Roland,

It is nice that the NFPA 13 committee has modified, however the lawyers will 
have a field day hanging the contractor out to dry since the contractor will be 
saying, in front of a jury, "that he did not follow the pipe manufacturer's UL 
listing because NFPA 13 (a consensus minimum level standard)    allowed him to 
not follow the UL listing" I do not think that NFPA 13 will get in front of the 
jury to say the NFPA 13 Committee will accept the liability. 

Jim Davidson 
 
Davidson Associates 
Fire Protection * Medical Gas * Code Consulting  
302-994-9500   Fax:302-234-1781


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Roland Huggins
Sent: Wednesday, February 29, 2012 6:16 PM
To: [email protected]
Subject: Re: Underground Pipe Material

Such removal would no longer be enforceable since it is explicitly  
addressed by 13.  This is another RARE case where the normal process  
(ie follow the cut-sheet requirements via the listing) is exempted by  
the technical committee.  Another example is the listed sprinklers  
required by 8.15.1.6 for concealed combustible spaces with a depth  
less than 36 in.  The listing applies only to solid wood joist but  
8.15.1.7 allows that sprinkler to be used with composite wood joists.

Roland

On Feb 29, 2012, at 2:47 PM, Jim Davidson wrote:

> You will need to check the UL listing of the pipe and the pipe  
> manufacturer's tech data regarding the loading the pipe can take  
> from building foundations and other loads such as traffic, truck  
> wheel loads on flexible pavement(asphalt), most of the underground  
> plastic pipe is not listed for use above ground, and you are  
> required to use a DI transition piece. I have seen AHJ require the  
> removal of the plastic pipe and replacement with DI transition  
> piece, very expensive after floor is poured and walls are up.
>
> Jim Davidson
>
> Jim Davidson
>
> Davidson Associates
> Fire Protection * Medical Gas * Code Consulting
> 302-994-9500   Fax:302-234-1781
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

Reply via email to