Greg,
I think that's going to change when the 2013 edition comes out. As
of right now, section 6.3.1.1.1 will read:
6.3.1.1.1* Underground pipe shall be permitted to extend into the
building through the slab or wall not more than 24 inches.
The annex note reads:
A.6.3.1.1.1 Extending the underground into a building provides working
room to transition to the appropriate above ground piping. Environmental
conditions should be considered as outlined in 23.1.6.1.2
That was voted on in the report on comments, 13-79, Log 34.
Interesting, to say the least.
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[email protected] <mailto:[email protected]>e-mail
www.ParsleyConsulting.com <http://www.ParsleyConsulting.com>website
On 2/29/2012 12:58 PM, Gregg Key wrote:
The C-900 pipe is approved and listed for underground use and not above
ground usage. Not suppose to use it to come up thru the floor.
C.Gregg Key, SET
Key Fire Protection Services,Inc
Project Manager
(O) 706-790-3473
(C) 706-220-8821
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Letterman,
Todd
Sent: Tuesday, February 28, 2012 12:57 PM
To: '[email protected]'
Subject: Re: Underground Pipe Material
Ok thanks good to know
----- Original Message -----
From: Cahill, Christopher [mailto:[email protected]]
Sent: Tuesday, February 28, 2012 09:52 AM
To: [email protected]<[email protected]>
Subject: RE: Underground Pipe Material
Never looked. Many places don't use NFPA 24 as an adopted code. Nearly all
(that have a code) use some version of NFPA 13. So it's a more reliable
reference for enforcement. I suppose in a standpipe situation the 13
reference wouldn't do much good but never ran into that question.
Chris Cahill, PE*
Senior Fire Protection Engineer, Aviation& Facilities Group Burns&
McDonnell
8201 Norman Center Drive
Bloomington, MN 55437
Phone: 952.656.3652
Fax: 952.229.2923
[email protected]
www.burnsmcd.com
Proud to be one of FORTUNE's 100 Best Companies to Work For *Registered in:
MN
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Letterman,
Todd
Sent: Tuesday, February 28, 2012 11:46 AM
To: '[email protected]'
Subject: Re: Underground Pipe Material
Hey Christopher is that a mirrored section reference in NFPA 24?
----- Original Message -----
From: Cahill, Christopher [mailto:[email protected]]
Sent: Tuesday, February 28, 2012 09:41 AM
To: [email protected]<[email protected]>
Subject: RE: Underground Pipe Material
NFPA 13 23.1.6.1.2 The transition piece shall be protected against possible
damage from corrosive agents, solvent attack, or mechanical damage.
It is generally interpreted to mean you can't use C900 or plastic through
the floor. Although I have seen AHJ's approve with a metal sleeve around it
up to the transition to steel.
Chris Cahill, PE*
Senior Fire Protection Engineer, Aviation& Facilities Group Burns&
McDonnell
8201 Norman Center Drive
Bloomington, MN 55437
Phone: 952.656.3652
Fax: 952.229.2923
[email protected]
www.burnsmcd.com
Proud to be one of FORTUNE's 100 Best Companies to Work For *Registered in:
MN
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Jimmy Waite
Sent: Tuesday, February 28, 2012 11:07 AM
To: [email protected]
Subject: Underground Pipe Material
When underground pipe passes under a foundation and stubs up into a
building, does the pipe have to be Ductile Iron? I know that's all I've
ever seen, but can C900 PVC pipe be used?
I've browsed through the International Plumbing Code and didn't find any
discussions about this situation.
Thanks,
Jimmy Waite, CET
Design Engineer
<mailto:[email protected]> [email protected]
mobile: 919.622.7030
cid:[email protected]
3609 Bastion Lane | Raleigh, NC 27604 | ': 919.212.2356 | 6:
919.212.2357 |<http://www.piedmontfire.com/> www.piedmontfire.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20120228/deaacbfa/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 5814 bytes
Desc: not available
URL:
<http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment
s/20120228/deaacbfa/attachment.jpg>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum