You will need to check the UL listing of the pipe and the pipe manufacturer's tech data regarding the loading the pipe can take from building foundations and other loads such as traffic, truck wheel loads on flexible pavement(asphalt), most of the underground plastic pipe is not listed for use above ground, and you are required to use a DI transition piece. I have seen AHJ require the removal of the plastic pipe and replacement with DI transition piece, very expensive after floor is poured and walls are up.
Jim Davidson Jim Davidson Davidson Associates Fire Protection * Medical Gas * Code Consulting 302-994-9500 Fax:302-234-1781 -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of ParsleyConsulting Sent: Wednesday, February 29, 2012 4:45 PM To: [email protected] Subject: Re: Underground Pipe Material Greg, I think that's going to change when the 2013 edition comes out. As of right now, section 6.3.1.1.1 will read: 6.3.1.1.1* Underground pipe shall be permitted to extend into the building through the slab or wall not more than 24 inches. The annex note reads: A.6.3.1.1.1 Extending the underground into a building provides working room to transition to the appropriate above ground piping. Environmental conditions should be considered as outlined in 23.1.6.1.2 That was voted on in the report on comments, 13-79, Log 34. Interesting, to say the least. PARSLEY CONSULTING Ken Wagoner, SET 760.745.6181 voice 760.745.0537 fax [email protected] <mailto:[email protected]>e-mail www.ParsleyConsulting.com <http://www.ParsleyConsulting.com>website On 2/29/2012 12:58 PM, Gregg Key wrote: > The C-900 pipe is approved and listed for underground use and not above > ground usage. Not suppose to use it to come up thru the floor. > > C.Gregg Key, SET > Key Fire Protection Services,Inc > Project Manager > (O) 706-790-3473 > (C) 706-220-8821 > > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of Letterman, > Todd > Sent: Tuesday, February 28, 2012 12:57 PM > To: '[email protected]' > Subject: Re: Underground Pipe Material > > Ok thanks good to know > > ----- Original Message ----- > From: Cahill, Christopher [mailto:[email protected]] > Sent: Tuesday, February 28, 2012 09:52 AM > To: [email protected]<[email protected]> > Subject: RE: Underground Pipe Material > > Never looked. Many places don't use NFPA 24 as an adopted code. Nearly all > (that have a code) use some version of NFPA 13. So it's a more reliable > reference for enforcement. I suppose in a standpipe situation the 13 > reference wouldn't do much good but never ran into that question. > > Chris Cahill, PE* > Senior Fire Protection Engineer, Aviation& Facilities Group Burns& > McDonnell > 8201 Norman Center Drive > Bloomington, MN 55437 > Phone: 952.656.3652 > Fax: 952.229.2923 > [email protected] > www.burnsmcd.com > > Proud to be one of FORTUNE's 100 Best Companies to Work For *Registered in: > MN > > > > > > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of Letterman, > Todd > Sent: Tuesday, February 28, 2012 11:46 AM > To: '[email protected]' > Subject: Re: Underground Pipe Material > > Hey Christopher is that a mirrored section reference in NFPA 24? > > ----- Original Message ----- > From: Cahill, Christopher [mailto:[email protected]] > Sent: Tuesday, February 28, 2012 09:41 AM > To: [email protected]<[email protected]> > Subject: RE: Underground Pipe Material > > NFPA 13 23.1.6.1.2 The transition piece shall be protected against possible > damage from corrosive agents, solvent attack, or mechanical damage. > > It is generally interpreted to mean you can't use C900 or plastic through > the floor. Although I have seen AHJ's approve with a metal sleeve around it > up to the transition to steel. > > Chris Cahill, PE* > Senior Fire Protection Engineer, Aviation& Facilities Group Burns& > McDonnell > 8201 Norman Center Drive > Bloomington, MN 55437 > Phone: 952.656.3652 > Fax: 952.229.2923 > [email protected] > www.burnsmcd.com > > Proud to be one of FORTUNE's 100 Best Companies to Work For *Registered in: > MN > > > > > > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of Jimmy Waite > Sent: Tuesday, February 28, 2012 11:07 AM > To: [email protected] > Subject: Underground Pipe Material > > When underground pipe passes under a foundation and stubs up into a > building, does the pipe have to be Ductile Iron? I know that's all I've > ever seen, but can C900 PVC pipe be used? > > > > I've browsed through the International Plumbing Code and didn't find any > discussions about this situation. > > > > > > Thanks, > > > > Jimmy Waite, CET > > Design Engineer > > > <mailto:[email protected]> [email protected] > > mobile: 919.622.7030 > > > > cid:[email protected] > > 3609 Bastion Lane | Raleigh, NC 27604 | ': 919.212.2356 | 6: > 919.212.2357 |<http://www.piedmontfire.com/> www.piedmontfire.com > > > > -------------- next part -------------- > An HTML attachment was scrubbed... > URL: > <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment > s/20120228/deaacbfa/attachment.html> > -------------- next part -------------- > A non-text attachment was scrubbed... > Name: image001.jpg > Type: image/jpeg > Size: 5814 bytes > Desc: not available > URL: > <http://fireball.firesprinkler.org/mailman/private/sprinklerforum/attachment > s/20120228/deaacbfa/attachment.jpg> > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum