I have seen the problem many times. The building owner wants to lease space.
He ignores the fact that the ordinary pipe schedule system is not meant for
20 ft. storage. The tenant does not know the system is deficient for rack
storage. Rack salesmen usually don't know or care that the building is not
meant for storage. I have done many sprinkler assessments over the years and
designed the necessary hydraulic upgrade to the system. This is a building
code issue. There needs to be a mandatory assessment when the tenant change
occurs and at 3-5 years intervals thereafter per NFPA 25.


Art Tiroly
ATCO Fire Protection/Tiroly
24400 Highland Rd CLE 44143
216-621-8899
216-570-7030 cell



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Roland
Huggins
Sent: Wednesday, November 06, 2013 10:13 AM
To: [email protected]
Subject: Re: NFPA25 scope

ACtually this issue is much broader than NFPA 25.  NFPA is asking the
question, what if anything that it do to reduce the number of failures of
the sprinkler system to control the fire (due to changes of contents changes
in the water supply, etc where the water discharge is not enough to control
the fire).  One of the question is should verifying the adequacy of the
sprinkler system be part of an NFPA 25 inspection or some other NFPA
document?

That is the starting point for this thread.  What do you gals and guys
think?

Roland

Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org





On Nov 5, 2013, at 10:09 PM, "Douglas Hicks" <[email protected]> wrote:

>
http://www.nfpa.org/newsandpublications/nfpa-journal/2013/november-december-
2013/features/closer-look?order_src=C246
> 
> More on 25 and the scope of 25.
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to