Ditto...NFPA 3 and 4 may pick up the slack.  If I was a fire marshal without
money or resources, I sure'd be looking long and hard at what I could get
from yearly audits of the life safety systems from a qualified / certified
firm.  Its not just about 25...

Steven Scandaliato, SET CFPS
520.971.2322 Cell
Skype: steven.scandaliato

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Roland
Huggins
Sent: Friday, November 08, 2013 1:19 PM
To: [email protected]
Subject: Re: NFPA25 scope

I agree there are PROBLEMS but I don't see a total disagreement in what you
wrote.  Maybe it's in how we fix the problem.  My adamant position is that
it is a code enforcement issue, not an NFPA issue and damn sure not a NFPA
25 issue.

Roland


Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org





On Nov 7, 2013, at 1:14 PM, Scott A Futrell <[email protected]> wrote:

> IMHO Roland, if I understand you correctly, I respectfully totally
disagree.  We do not have anything in place, at any level, to verify the
design, installation, inspection, testing, or maintenance of existing or new
sprinkler systems.  Technically, the legally adopted Fire Codes give the AHJ
the power and authority, but they don't have the time, money, or people
power to thoroughly review plans, inspect structures, and then review and
inspect inspection, testing, and maintenance reports. Contractors don't do
their own peer reviews before sending out plans or reviewing their own
installations.  Engineers (except for some FPE's) don't review
installations.  Owners don't have a clue about IT&M requirements and how
changes they or hired GC's affect sprinkler systems, and field inspections
will not turn up the things others have mentioned and I see frequently.
EVEN if you give the owner a copy of NFPA 25 what percentage of them
understand everything in the Standard and every i
 mplication to their system(s).  The things I see very frequently do end up
costing contractors (because they screwed up OR defending themselves when
they did it right) and owners (because it was wrong originally, they weren't
told, OR because they didn't do something(s) they should have) a great deal
of time and money because someone hasn't done something that IS in the
Standard. Insurance pays for a lot, but insurance goes up and insurance
doesn't cover all the lost time and revenue.
> 
> See you in Chicago? It should be spirited!
> 
> Scott Futrell
>  

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to