Its in the PA UCC, which he's operating under.  It was added to the 2009
edition after they took out the residential sprinkler requirement.

Its also now included in the 2012 edition of the IRC.

We prefer to not call it a sprinkler system, but as a fire rating
equivalency.

Richard, I remember George calling these 'Maytag' systems since they only
protect the washer and dryer.

I had a change of heart when I realized that this is a foothold into
people's homes.  If they've already got sprinklers in the basement, more
may opt to have them installed throughout.

And if there's one thing I've learned from doing a lot of single family
homes, its that the only other trade that's hated more than the sprinkler
guy is the drywall guy.  Drywall the basement you say?  Guess who gets
called out the first time there's a small leak.  You would be surprised how
competitive you can be versus the drywaller if you can make the system work
off the existing service.

Again, this is all on the up and up.  Check the 2012 IRC.

http://publicecodes.cyberregs.com/icod/irc/2012/icod_irc_2012_5_sec001.htm
*R501.3 Fire protection of floors. *
Floor assemblies, not required elsewhere in this code to be fire-resistance
rated, shall be provided with a 1/2-inch (12.7 mm) gypsum wallboard
membrane, 5/8-inch (16 mm) wood structural panel membrane, or equivalent on
the underside of the floor framing member.

*Exceptions: *

1. Floor assemblies located directly over a space protected by an automatic
sprinkler system in accordance with Section P2904, NFPA13D, or other
approved equivalent sprinkler system. 2. Floor assemblies located directly
over a crawl space not intended for storage or fuel-fired appliances. 3.
Portions of floor assemblies can be unprotected when complying with the
following: 3.1. The aggregate area of the unprotected portions shall not
exceed 80 square feet per story 3.2. Fire blocking in accordance with Section
R302.11.1 shall be installed along the perimeter of the unprotected portion
to separate the unprotected portion from the remainder of the floor
assembly. 4. Wood floor assemblies using dimension lumber or structural
composite lumber equal to or greater than 2-inch by 10-inch (50.8 mm by 254
mm) nominal dimension, or other approved floor assemblies demonstrating
equivalent fire performance.