The AHJ is telling the builder that if they had used conventional framing IE, 
2"x12" @ 16 oc there would not be an issue. He says that the TJI's will burn 
faster than conventional framing therefore he wants them protected by dry wall, 
fire proofing or sprinklers.

Richard L. Mote
Rowe Sprinkler Systems, Inc.
7994 Route 522, Suite 1
PO Box 407
Middleburg, PA 17842
P 570-837-7647
F 570-837-6335

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Sprinkler 
Design Services
Sent: Thursday, December 05, 2013 3:35 PM
To: [email protected]
Subject: RE: NFPA 13D or 13?

It seems like it would be massive overkill to design this per 13, so I'd do the 
design for 13D. It might be prudent to ask the AHJ for his opinion since he 
seems to modifying the rules at his fancy.

Marc Walter, SET
Sprinkler Design Services
Seaside, OR 97138
(503) 956-4019

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Richard 
Mote
Sent: Thursday, December 05, 2013 12:12 PM
To: [email protected]
Subject: NFPA 13D or 13?

I guess I will have to show my ignorance, I can count on one hand the number of 
13D systems I have designed in the last 10 years. This project is a 13D single 
family custom home with a basement of 2746 sq. ft. the AHJ is requiring that 
the basement be sprinklered, but he isn't requiring the rest of the house to 
have sprinklers. Since this would normally be part of a 13D system do I just do 
a 2 head calculation and call it done? Or do I calculate a 900 sq. ft. area, 
per 13. (It does meet all the criteria for area
reduction) My thinking is that even though the basement could be protected per 
13D if the entire house was covered, since this is a special requirement by the 
AHJ I should calculate per 13. BTW the 2007 codes are the applicable standards 
at this time. The owner is going to have to install tanks and a pump so the 
difference in demand is a big deal.


Richard L. Mote CET
Rowe Sprinkler Systems, Inc.
7994 Route 522, Suite 1
PO Box 407
Middleburg, PA 17842
P 570-837-7647
F 570-837-6335

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to