House is on a private well, so if we do put in sprinklers it's 2 300 gallon 
tanks and a 53 gpm @ 43 psi pump.

Richard L. Mote
Rowe Sprinkler Systems, Inc.
7994 Route 522, Suite 1
PO Box 407
Middleburg, PA 17842
P 570-837-7647
F 570-837-6335

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Ben Young
Sent: Thursday, December 05, 2013 5:09 PM
To: [email protected]
Subject: Re: NFPA 13D or 13?

Its in the PA UCC, which he's operating under.  It was added to the 2009 
edition after they took out the residential sprinkler requirement.

Its also now included in the 2012 edition of the IRC.

We prefer to not call it a sprinkler system, but as a fire rating equivalency.

Richard, I remember George calling these 'Maytag' systems since they only 
protect the washer and dryer.

I had a change of heart when I realized that this is a foothold into people's 
homes.  If they've already got sprinklers in the basement, more may opt to have 
them installed throughout.

And if there's one thing I've learned from doing a lot of single family homes, 
its that the only other trade that's hated more than the sprinkler guy is the 
drywall guy.  Drywall the basement you say?  Guess who gets called out the 
first time there's a small leak.  You would be surprised how competitive you 
can be versus the drywaller if you can make the system work off the existing 
service.

Again, this is all on the up and up.  Check the 2012 IRC.

http://publicecodes.cyberregs.com/icod/irc/2012/icod_irc_2012_5_sec001.htm
*R501.3 Fire protection of floors. *
Floor assemblies, not required elsewhere in this code to be fire-resistance 
rated, shall be provided with a 1/2-inch (12.7 mm) gypsum wallboard membrane, 
5/8-inch (16 mm) wood structural panel membrane, or equivalent on the underside 
of the floor framing member.

*Exceptions: *

1. Floor assemblies located directly over a space protected by an automatic 
sprinkler system in accordance with Section P2904, NFPA13D, or other approved 
equivalent sprinkler system. 2. Floor assemblies located directly over a crawl 
space not intended for storage or fuel-fired appliances. 3.
Portions of floor assemblies can be unprotected when complying with the
following: 3.1. The aggregate area of the unprotected portions shall not exceed 
80 square feet per story 3.2. Fire blocking in accordance with Section
R302.11.1 shall be installed along the perimeter of the unprotected portion to 
separate the unprotected portion from the remainder of the floor assembly. 4. 
Wood floor assemblies using dimension lumber or structural composite lumber 
equal to or greater than 2-inch by 10-inch (50.8 mm by 254
mm) nominal dimension, or other approved floor assemblies demonstrating 
equivalent fire performance.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to