NFPA 1 (2003)
1.1 Scope
1.1.1 The scope includes, but not limited to, the following:

(14) Conditions affecting fire fighter safety


Seems TJI's are a BIG fire fighter concern.
In my opinion all un-sprinklered homes built with TJI's should have a
special designation on it (Scarlet Letter) so when the FF's show up then
can kick back and pull out the hotdogs and marshmallows and watch it burn.
After of course, they are sure nobody is in the house.


David Autry

Meininger Fire Protection Inc.
2521 W L St. Suite No.4
Lincoln, Ne 68522
Voice (402) 466-2616
Fax (402) 466-2617
[email protected]


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
Cahill, Christopher
Sent: Thursday, December 05, 2013 3:00 PM
To: [email protected]
Subject: RE: NFPA 13D or 13?

If you are using NFPA 1 or IRC it appears sprinklers are required in the
building or the 2,500 sq.ft. basement thing.  I'm not seeing where a
construction type is a factor.  I fully defer to those actually use NFPA 1
or IRC regularly if I'm wrong.

AHJ is entirely correct they do burn faster.  But unless you have a LAW
(code) identifying the issue of conventional framing is OK but lightweight
requires protection the owner does not have to protect it.  I realize then
you are suggesting to the owner a reason not to hire you and that's bad
for business.

My couch also burns faster than my Grandmothers couch but I don't have to
sprinkler. Hey tell him/her logic is flawed in that conventional lumber
burns faster than steel so conventional should also be protected too.  And
steel burns faster than rock so unless you move into a cave it must need
protection.

Chris Cahill, PE*
Senior Fire Protection Engineer
Burns & McDonnell
8201 Norman Center Drive
Bloomington, MN 55437
Phone:  952.656.3652
Fax:  952.229.2923
[email protected]
www.burnsmcd.com

Proud to be one of FORTUNE's 100 Best Companies to Work For *Registered
in: MN





-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
Richard Mote
Sent: Thursday, December 05, 2013 2:40 PM
To: [email protected]
Subject: RE: NFPA 13D or 13?

The AHJ is telling the builder that if they had used conventional framing
IE, 2"x12" @ 16 oc there would not be an issue. He says that the TJI's
will burn faster than conventional framing therefore he wants them
protected by dry wall, fire proofing or sprinklers.

Richard L. Mote
Rowe Sprinkler Systems, Inc.
7994 Route 522, Suite 1
PO Box 407
Middleburg, PA 17842
P 570-837-7647
F 570-837-6335

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
Sprinkler Design Services
Sent: Thursday, December 05, 2013 3:35 PM
To: [email protected]
Subject: RE: NFPA 13D or 13?

It seems like it would be massive overkill to design this per 13, so I'd
do the design for 13D. It might be prudent to ask the AHJ for his opinion
since he seems to modifying the rules at his fancy.

Marc Walter, SET
Sprinkler Design Services
Seaside, OR 97138
(503) 956-4019

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
Richard Mote
Sent: Thursday, December 05, 2013 12:12 PM
To: [email protected]
Subject: NFPA 13D or 13?

I guess I will have to show my ignorance, I can count on one hand the
number of 13D systems I have designed in the last 10 years. This project
is a 13D single family custom home with a basement of 2746 sq. ft. the AHJ
is requiring that the basement be sprinklered, but he isn't requiring the
rest of the house to have sprinklers. Since this would normally be part of
a 13D system do I just do a 2 head calculation and call it done? Or do I
calculate a 900 sq. ft. area, per 13. (It does meet all the criteria for
area
reduction) My thinking is that even though the basement could be protected
per 13D if the entire house was covered, since this is a special
requirement by the AHJ I should calculate per 13. BTW the 2007 codes are
the applicable standards at this time. The owner is going to have to
install tanks and a pump so the difference in demand is a big deal.


Richard L. Mote CET
Rowe Sprinkler Systems, Inc.
7994 Route 522, Suite 1
PO Box 407
Middleburg, PA 17842
P 570-837-7647
F 570-837-6335

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.o
rg

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.o
rg
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.o
rg
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.o
rg
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to