Aha thanks Spencer.

I was just sent this too:

7.3.1.7.4*   A separate additional indicating control valve, supervised in
accordance with 8.16.1.1.2, shall be permitted to be installed in the riser
assembly above a preaction or deluge valve to permit full function trip
testing as required by NFPA 25, without flooding the system.

A.7.3.1.7.4  Preaction and deluge valves should be fully trip tested
wherever possible. Providing a functional trip test without waterflow does
not reveal other potential problems such as obstructions and/or misaligned
nozzles.

thanks again,

Brad

-----Original Message-----
From: Spencer Allen [mailto:[email protected]] 
Sent: Monday, August 25, 2014 10:39 AM
To: [email protected]
Subject: RE: two control valves in a deluge system riser?

Partial Trip Test?

I have installed these on pre-action and deluge before.  Very useful when
testing the activation pre-comissioning.

Best Regards,

Spencer Allen

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Brad Casterline
Sent: 25 August 2014 16:35
To: [email protected]
Subject: two control valves in a deluge system riser?

Co-worker is looking at a contractor's riser detail. Systems are straight
water deluge, protec-o-wire (electric activation).

There is a BF control valve at the header AND one on top of the deluge
valve.

Exhibit 7.8, page 210 of NFPA 13 2013 handbook shows something similar.  

Does anyone know the reason for two control valves?

 

thanks,

 

Brad Casterline, NICET IV

Fire Protection Division

 

FSC, Inc.

P: 913-722-3473

[email protected]

www.fsc-inc.com

 

Engineering Solutions for the Built Environment

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to