Thanks Richard!

-----Original Message-----
From: Richard Mote [mailto:[email protected]] 
Sent: Monday, August 25, 2014 10:48 AM
To: [email protected]
Subject: RE: two control valves in a deluge system riser?

What he said, I've called for them on freezer systems so they can be can
trip tested without filling the entire system.
I have also used them on fixed water spray systems in situations where you
really don't water on what your protecting unless it's on fire. For example
transformers, coal conveyers, bearing boxes, burner fronts and the like.

Richard L. Mote ET
Design Manager
Rowe Sprinkler Systems, Inc.



-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Spencer Allen
Sent: Monday, August 25, 2014 11:39 AM
To: [email protected]
Subject: RE: two control valves in a deluge system riser?

Partial Trip Test?

I have installed these on pre-action and deluge before.  Very useful when
testing the activation pre-comissioning.

Best Regards,

Spencer Allen

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Brad Casterline
Sent: 25 August 2014 16:35
To: [email protected]
Subject: two control valves in a deluge system riser?

Co-worker is looking at a contractor's riser detail. Systems are straight
water deluge, protec-o-wire (electric activation).

There is a BF control valve at the header AND one on top of the deluge
valve.

Exhibit 7.8, page 210 of NFPA 13 2013 handbook shows something similar.  

Does anyone know the reason for two control valves?

 

thanks,

 

Brad Casterline, NICET IV

Fire Protection Division

 

FSC, Inc.

P: 913-722-3473

[email protected]

www.fsc-inc.com

 

Engineering Solutions for the Built Environment

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to