So as the N2 is absorbed by the antifreeze, is there any loss of volume (and 
subsequent reduction in pressure) in the piping that would allow water to 
migrate into the AF lines? If so, how much? Or does the 'Nitrogenated' AF 
solution simply expand to occupy the space held by the pure N2 under the same 
pressure?

Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection Engineer | 
Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 | 
http://www.kfiengineers.com

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]
Sent: Thursday, November 13, 2014 11:32 AM
To: [email protected]
Subject: RE: Antifreeze-recipe for disaster?

I would bet the nitrogen never "leaks out of the system", based on Henry's Law, 
as the nitrogen dissolves into solution under pressure. And by using nitrogen 
as the pressurizing agent, no increase in oxidation (corrosion) is imparted. 
I'm aware that nitrogen has been used to pressurize sprinkler piping for 
various reasons for at least thirty years.
Mark at Aero

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Mark A. Sornsin, P.E.
Sent: Thursday, November 13, 2014 9:01 AM
To: [email protected]
Subject: RE: Antifreeze-recipe for disaster?

C'mon, Todd.  WHY is he the missing link?


...because there is no way of know with certainty how much water will enter the 
AF piping after all of the N2 eventually leaks out. The presents the 
possibility of a freezable AF system. I suppose one could calculate the exact 
volume of the AF piping and measure the exact amount of AF pumped into the 
system prior to charging with N2, proving that the water couldn't migrate too 
far.... I would hope that approach was well documented prior to the freeze 
event and lawsuit.

Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection Engineer | 
Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 | 
http://www.kfiengineers.com

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Todd Williams
Sent: Wednesday, November 12, 2014 8:13 PM
To: [email protected]
Subject: Re: Antifreeze-recipe for disaster?

No, but I think the guy that did it is the missing link.

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080
www.fpdc.com


> On Nov 12, 2014, at 8:58 PM, Thomas Watt <[email protected]> 
> wrote:
>
> I recently encountered a scenario which I felt this group would enjoy
> chewing on.
> While draining an AF system to replace another leaking(@brass/steel
> interface) no-torque head adapter, huge bursts of mist, aerosolized
> glycerin mix, came out.
> It seems that this company has an s.o.p. of pumping af into dead end
> system(no purge) using a cheap pump which only permits about 50psi.
> They then jack the system pressure above static with compressed nitrogen.
> Has anybody ever seen this done before? Am I off base here or is this
> possibly the missing link?
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com 
______________________________________________________________________

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com 
______________________________________________________________________
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com 
______________________________________________________________________

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to