The testing didn't include that, but certainly pressure and atomization were 
contributing regardless of how it happens. 

Scott
 
(763) 425-1001x12 Office
(612) 759-5556 Cell

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Thomas Watt
Sent: Friday, November 14, 2014 2:00 PM
To: [email protected]
Subject: RE: Antifreeze-recipe for disaster?

I was hoping you would offer input Scott. I noticed your name in the report as 
I read it. I just did not see any inference to escaping gases contributing to 
the smaller droplet size which are shown to be flammable/explosive. Perhaps 
because gas pockets are not supposed to be there?
On Nov 14, 2014 12:48 PM, "Scott A Futrell" <[email protected]> wrote:

> In short, the theory was tested and it is combination of concentration 
> of PG or Glycerin, type of sprinkler, orifice size, pressure, and 
> distance to ignition source and is all available on the Fire 
> Protection Research Foundation website.
>
> Scott
>
> (763) 425-1001x12 Office
> (612) 759-5556 Cell
>
> -----Original Message-----
> From: Sprinklerforum [mailto:
> [email protected]] On Behalf Of Thomas 
> Watt
> Sent: Friday, November 14, 2014 1:35 PM
> To: [email protected]
> Subject: Re: Antifreeze-recipe for disaster?
>
> The point I was trying to make is  the aerosolization of the 
> antifreeze by the velocity of escaping air and gas. Could this be the 
> cause of the explosion incidents? Has this scenario been tested?
> On Nov 13, 2014 11:07 AM, <[email protected]> wrote:
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org