In short, the theory was tested and it is combination of concentration of PG or 
Glycerin, type of sprinkler, orifice size, pressure, and distance to ignition 
source and is all available on the Fire Protection Research Foundation website.

Scott
 
(763) 425-1001x12 Office
(612) 759-5556 Cell

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Thomas Watt
Sent: Friday, November 14, 2014 1:35 PM
To: [email protected]
Subject: Re: Antifreeze-recipe for disaster?

The point I was trying to make is  the aerosolization of the antifreeze by the 
velocity of escaping air and gas. Could this be the cause of the explosion 
incidents? Has this scenario been tested?
On Nov 13, 2014 11:07 AM, <[email protected]> wrote: