I think the point that Todd is trying to make is that normally the air is
purged from the all the pipes on an Antifreeze system. 
Sounds like poor workmanship to me.

Regards,
G. Tim Stone

G. Tim Stone Consulting, LLC
NICET Level III Engineering Technician
Fire Protection Sprinkler Design
and Consulting Services

                117 Old Stage Rd. - Essex Jct., VT. 05452
CELL: (802) 373-0638   TEL: (802) 434-2968   Fax: (802) 434-4343
                           [email protected]

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Mark A. Sornsin, P.E.
Sent: Thursday, November 13, 2014 12:41 PM
To: [email protected]
Subject: RE: Antifreeze-recipe for disaster?

So as the N2 is absorbed by the antifreeze, is there any loss of volume (and
subsequent reduction in pressure) in the piping that would allow water to
migrate into the AF lines? If so, how much? Or does the 'Nitrogenated' AF
solution simply expand to occupy the space held by the pure N2 under the
same pressure?

Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection
Engineer | Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 |
http://www.kfiengineers.com

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of [email protected]
Sent: Thursday, November 13, 2014 11:32 AM
To: [email protected]
Subject: RE: Antifreeze-recipe for disaster?

I would bet the nitrogen never "leaks out of the system", based on Henry's
Law, as the nitrogen dissolves into solution under pressure. And by using
nitrogen as the pressurizing agent, no increase in oxidation (corrosion) is
imparted. I'm aware that nitrogen has been used to pressurize sprinkler
piping for various reasons for at least thirty years.
Mark at Aero

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Mark A. Sornsin, P.E.
Sent: Thursday, November 13, 2014 9:01 AM
To: [email protected]
Subject: RE: Antifreeze-recipe for disaster?

C'mon, Todd.  WHY is he the missing link?


...because there is no way of know with certainty how much water will enter
the AF piping after all of the N2 eventually leaks out. The presents the
possibility of a freezable AF system. I suppose one could calculate the
exact volume of the AF piping and measure the exact amount of AF pumped into
the system prior to charging with N2, proving that the water couldn't
migrate too far.... I would hope that approach was well documented prior to
the freeze event and lawsuit.

Mark A. Sornsin, P.E. | Karges-Faulconbridge, Inc. | Fire Protection
Engineer | Fargo, ND | direct: 701.552.9905 | mobile: 701.371.5759 |
http://www.kfiengineers.com

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Todd Williams
Sent: Wednesday, November 12, 2014 8:13 PM
To: [email protected]
Subject: Re: Antifreeze-recipe for disaster?

No, but I think the guy that did it is the missing link.

Todd G Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860-535-2080
www.fpdc.com


> On Nov 12, 2014, at 8:58 PM, Thomas Watt
<[email protected]> wrote:
>
> I recently encountered a scenario which I felt this group would enjoy 
> chewing on.
> While draining an AF system to replace another leaking(@brass/steel
> interface) no-torque head adapter, huge bursts of mist, aerosolized 
> glycerin mix, came out.
> It seems that this company has an s.o.p. of pumping af into dead end 
> system(no purge) using a cheap pump which only permits about 50psi.
> They then jack the system pressure above static with compressed nitrogen.
> Has anybody ever seen this done before? Am I off base here or is this 
> possibly the missing link?
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to