look at 8.3.3.2 - if QR is used, all sprinklers within that COMPARTMENT must be 
QR.

Also not that some EC (aka 20 x 20) with a fast response link are not QR.

Roland

Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>





> On Dec 18, 2014, at 8:57 AM, Vince Sabolik <[email protected]> wrote:
> 
> Hi forum ... this hurting my brain today.
> 
> If standard response sprinklers are installed in a given space - a retail 
> tenant,
> can QR extended heads be used in a subsequent addition. The two areas will 
> have the same ceiling
> and I want to use extended heads in the addition because of intense surface 
> strip lighting.