If the intent for this section were to also consider the standard-response 
spaced sprinklers as being declared quick-response then it would have also 
stated that in addition to stating they could be mixed within the same 
compartment. Mixing them in this way means quick response has not been used 
throughout as is required by some building codes for various situations. The 
installation could wind up not building code compliant.

Allan Seidel
St. Louis, MO


> On Dec 18, 2014, at 12:53 PM, Pete Schwab <[email protected]> wrote:
> 
> For the 2016 edition, the following language should appear
> 
> 8.3.3.5 
> Where a sprinkler carries a listing for both standard-response protection and 
> quick-response protection at different coverage areas, that sprinkler shall 
> be permitted to be installed within a compartment at the spacing for both the 
> quick- response and standard-response listings without any separation between 
> the areas so covered.
> 
> Peter Schwab
> VP of Purchasing & Engineering Technologies
> 
> Wayne Automatic Fire Sprinklers Inc.
> 222 Capitol Court
> Ocoee, Fl 34761
> 
> Mobile: (407) 468-8248
> Direct: (407) 877-5570
> Fax: (407) 656-8026
> 
> www.waynefire.com
> 
> 
> 
> We're hiring great people at all of our locations!  Please check out our 
> website for the details! 
> 
> -----Original Message-----
> From: Sprinklerforum [mailto:[email protected]] 
> On Behalf Of Roland Huggins
> Sent: Thursday, December 18, 2014 12:05 PM
> To: [email protected]
> Subject: Re: What's YOUR response??
> 
> look at 8.3.3.2 - if QR is used, all sprinklers within that COMPARTMENT must 
> be QR.
> 
> Also not that some EC (aka 20 x 20) with a fast response link are not QR.
> 
> Roland
> 
> Roland Huggins, PE - VP Engineering
> American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
> Dallas, TX
> http://www.firesprinkler.org <http://www.firesprinkler.org/>
> 
> 
> 
> 
> 
>> On Dec 18, 2014, at 8:57 AM, Vince Sabolik <[email protected]> wrote:
>> 
>> Hi forum ... this hurting my brain today.
>> 
>> If standard response sprinklers are installed in a given space - a 
>> retail tenant, can QR extended heads be used in a subsequent addition. 
>> The two areas will have the same ceiling and I want to use extended heads in 
>> the addition because of intense surface strip lighting.
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to