Good point Allan! My take is this: example 1-- Light Hazard-- Q.R. required-- Sprinkler= "Acme Model A" listed Q.R. at max 14 x 14 and S.R. up to 20 x 20-- so max spacing = 14 x 14. example 2-- Ord Haz-- same sprinkler-- max spacing = 20 x 20, BUT if it happens that some coverage areas are 14 X 14, it is NOT considered mixing Q.R. and S.R.
Brad -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of AKS-Gmail-IMAP Sent: Saturday, December 20, 2014 12:00 PM To: [email protected] Subject: Re: What's YOUR response?? If the intent for this section were to also consider the standard-response spaced sprinklers as being declared quick-response then it would have also stated that in addition to stating they could be mixed within the same compartment. Mixing them in this way means quick response has not been used throughout as is required by some building codes for various situations. The installation could wind up not building code compliant. Allan Seidel St. Louis, MO > On Dec 18, 2014, at 12:53 PM, Pete Schwab <[email protected]> wrote: > > For the 2016 edition, the following language should appear > > 8.3.3.5 > Where a sprinkler carries a listing for both standard-response protection and quick-response protection at different coverage areas, that sprinkler shall be permitted to be installed within a compartment at the spacing for both the quick- response and standard-response listings without any separation between the areas so covered. > > Peter Schwab > VP of Purchasing & Engineering Technologies > > Wayne Automatic Fire Sprinklers Inc. > 222 Capitol Court > Ocoee, Fl 34761 > > Mobile: (407) 468-8248 > Direct: (407) 877-5570 > Fax: (407) 656-8026 > > www.waynefire.com > > > > We're hiring great people at all of our locations! Please check out our website for the details! > > -----Original Message----- > From: Sprinklerforum [mailto:[email protected]] On Behalf Of Roland Huggins > Sent: Thursday, December 18, 2014 12:05 PM > To: [email protected] > Subject: Re: What's YOUR response?? > > look at 8.3.3.2 - if QR is used, all sprinklers within that COMPARTMENT must be QR. > > Also not that some EC (aka 20 x 20) with a fast response link are not QR. > > Roland > > Roland Huggins, PE - VP Engineering > American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives > Dallas, TX > http://www.firesprinkler.org <http://www.firesprinkler.org/> > > > > > >> On Dec 18, 2014, at 8:57 AM, Vince Sabolik <[email protected]> wrote: >> >> Hi forum ... this hurting my brain today. >> >> If standard response sprinklers are installed in a given space - a >> retail tenant, can QR extended heads be used in a subsequent addition. >> The two areas will have the same ceiling and I want to use extended heads in the addition because of intense surface strip lighting. > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org