I agree with Roland.  Most ECOH are not QR after you get past 14x14 or 16
x16 .  The only problem I can see is balancing the ECOH and the ssp.  The
high gallons needed for the ecoh will cause your ssp to overflow like crazy.
I can't tell you how many times this has been my remote area, while the
traditional remote area 100' away requires 3-4 psi less. 

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Roland Huggins
Sent: Thursday, December 18, 2014 12:05 PM
To: [email protected]
Subject: Re: What's YOUR response??

look at 8.3.3.2 - if QR is used, all sprinklers within that COMPARTMENT must
be QR.

Also not that some EC (aka 20 x 20) with a fast response link are not QR.

Roland

Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>





> On Dec 18, 2014, at 8:57 AM, Vince Sabolik <[email protected]> wrote:
> 
> Hi forum ... this hurting my brain today.
> 
> If standard response sprinklers are installed in a given space - a 
> retail tenant, can QR extended heads be used in a subsequent addition. 
> The two areas will have the same ceiling and I want to use extended heads
in the addition because of intense surface strip lighting.

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
For more information please visit http://www.symanteccloud.com
______________________________________________________________________

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to