I agree with Roland. Most ECOH are not QR after you get past 14x14 or 16 x16 . The only problem I can see is balancing the ECOH and the ssp. The high gallons needed for the ecoh will cause your ssp to overflow like crazy. I can't tell you how many times this has been my remote area, while the traditional remote area 100' away requires 3-4 psi less.
-----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Roland Huggins Sent: Thursday, December 18, 2014 12:05 PM To: [email protected] Subject: Re: What's YOUR response?? look at 8.3.3.2 - if QR is used, all sprinklers within that COMPARTMENT must be QR. Also not that some EC (aka 20 x 20) with a fast response link are not QR. Roland Roland Huggins, PE - VP Engineering American Fire Sprinkler Assn. --- Fire Sprinklers Saves Lives Dallas, TX http://www.firesprinkler.org <http://www.firesprinkler.org/> > On Dec 18, 2014, at 8:57 AM, Vince Sabolik <[email protected]> wrote: > > Hi forum ... this hurting my brain today. > > If standard response sprinklers are installed in a given space - a > retail tenant, can QR extended heads be used in a subsequent addition. > The two areas will have the same ceiling and I want to use extended heads in the addition because of intense surface strip lighting. _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org ______________________________________________________________________ This email has been scanned by the Symantec Email Security.cloud service. For more information please visit http://www.symanteccloud.com ______________________________________________________________________ _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org