Good job on this issue by the Public In Putters and T.C. Members.

I followed up on the additional proposed language about not mixing thermal
response in the same area. There are a couple exceptions (as far as I
looked):
1. Quick Response are allowed in racks where overhead is Standard Response.
2. QR allowed under overhead doors where overhead is SR.

Brad 

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Steve Leyton
Sent: Thursday, December 18, 2014 1:10 PM
To: [email protected]
Subject: RE: What's YOUR response??

Right.  So in some states you'll be able to creatively apply mixed
sprinklers in ... 2020, if then.

SL


-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Pete Schwab
Sent: Thursday, December 18, 2014 10:54 AM
To: [email protected]
Subject: RE: What's YOUR response??

For the 2016 edition, the following language should appear

8.3.3.5
Where a sprinkler carries a listing for both standard-response protection
and quick-response protection at different coverage areas, that sprinkler
shall be permitted to be installed within a compartment at the spacing for
both the quick- response and standard-response listings without any
separation between the areas so covered.

Peter Schwab
VP of Purchasing & Engineering Technologies

Wayne Automatic Fire Sprinklers Inc.
222 Capitol Court
Ocoee, Fl 34761

Mobile: (407) 468-8248
Direct: (407) 877-5570
Fax: (407) 656-8026

www.waynefire.com



We're hiring great people at all of our locations!  Please check out our
website for the details! 

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Roland Huggins
Sent: Thursday, December 18, 2014 12:05 PM
To: [email protected]
Subject: Re: What's YOUR response??

look at 8.3.3.2 - if QR is used, all sprinklers within that COMPARTMENT must
be QR.

Also not that some EC (aka 20 x 20) with a fast response link are not QR.

Roland

Roland Huggins, PE - VP Engineering
American Fire Sprinkler Assn.       ---      Fire Sprinklers Saves Lives
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>





> On Dec 18, 2014, at 8:57 AM, Vince Sabolik <[email protected]> wrote:
> 
> Hi forum ... this hurting my brain today.
> 
> If standard response sprinklers are installed in a given space - a 
> retail tenant, can QR extended heads be used in a subsequent addition.
> The two areas will have the same ceiling and I want to use extended heads
in the addition because of intense surface strip lighting.

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to