A lot of the extended coverage sprinklers on the market use the same
sprinkler (i.e. exact same part number) for both the standard and quick
response listing. The only difference seems to be that some are limited in
their listed area of coverage for quick response.
Can you not install SR Extended coverage sprinklers (likely would be the
exact same sprinkler as if you were installing it as QR)? It would seem the
only advantage in using (i.e. calling it) a QR sprinkler would be to
utilise the reduction of remote area size. However, since you have the
existing as SR then I thought you wouldn't be able to do the remote area
reduction anyway?

As far as the 7psi minimum end head pressure...The minimum listed area of
coverage for QR sprinklers is generally 14x14. In looking at a datasheet in
treating as your Retail as OH2 would seem to require a minimum of 12.1psi
as part of the product listing.

Regards.

Damien Shannon.

On 18 December 2014 at 17:02, Steve Leyton <[email protected]>
wrote:
>
> I believe the answer is no.   You can mix standard and extended coverages
> but not RTI's.
>
> Steve Leyton
> PROTECTION DESIGN & CONSULTING
> 2851 Camino del Rio South, Suite 210
> San Diego, CA 92108
> -------------------------------------------
> Ph:   619.255.8964 - ext. 102
> Fax:  619.255.9364
> Cell: 619.972.5696
>
>
>
>
> -----Original Message-----
> From: Sprinklerforum [mailto:
> [email protected]] On Behalf Of Vince Sabolik
> Sent: Thursday, December 18, 2014 8:57 AM
> To: [email protected]
> Subject: What's YOUR response??
>
> Hi forum ... this hurting my brain today.
>
> If standard response sprinklers are installed in a given space - a retail
> tenant, can QR extended heads be used in a subsequent addition. The two
> areas will have the same ceiling and I want to use extended heads in the
> addition because of intense surface strip lighting.
>
> Also, does anyone know if an extended head can be used in a 12 x 12
> spacing @ 7 psi if the listing starts at 14 x 14?
>
> Thanks for any info!
>
>
>                                                       Vince
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>


-- 

*Damien Shannon*
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to