Thanks for confirming Jerry. The light is small and It just looks weird to have a head so far away from the center of the room where the light is located. Of course when I have to offset the sprinkler so much it affects my calculations since it is a 13 application. Glad the salesman bid it as if there were no lights present :) Thanks, Dewayne
-----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Jerry Van Kolken Sent: Thursday, April 09, 2015 6:49 PM To: [email protected] Subject: RE: NFPA 13 (07ed) apartment obstructions Looks like your you using the 4x rule . You should only need a single head at 36" away. Jerry Van Kolken Millennium Fire Protection (760) 722-2722 -----Original Message----- From: Sprinklerforum [mailto:[email protected]] On Behalf Of Dewayne Martinez Sent: Thursday, April 09, 2015 10:16 AM To: [email protected] Subject: NFPA 13 (07ed) apartment obstructions I am using residential concealed pendant sprinklers in a NFPA 13 apartment complex. Many of the rooms have a surface mounted domed light which is about 12in in diameter and 5in deep at the center. It seems to me that I must maintain at least 36in away from the edge of the light per figure 8.10.6.2.1.3 or install a sprinkler on both sides correct? Thanks, Dewayne _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.o rg _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.o rg _______________________________________________ Sprinklerforum mailing list [email protected] http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org