It would but I am using residential pendant sprinklers and the small room
rule only applies to standard throw sprinklers.
I guess that's the tradeoff I need to deal with for only wanting to calc 4
sprinklers and using extended coverage.

-----Original Message-----
From: Sprinklerforum
[mailto:[email protected]] On Behalf Of John
Denhardt
Sent: Monday, April 13, 2015 6:46 AM
To: <[email protected]>
Subject: Re: NFPA 13 (07ed) apartment obstructions

Does the small room apply?  If so, use .05 x small room rule or listing
whichever is larger.

Sprinklers Save

> On Apr 13, 2015, at 7:38 AM, Dewayne Martinez
<[email protected]> wrote:
>
> Thanks for confirming Jerry.  The light is small and It just looks
> weird to have a head so far away from the center of the room where the
> light is located.  Of course when I have to offset the sprinkler so
> much it affects my calculations since it is a 13 application.  Glad
> the salesman bid it as if there were no lights present :) Thanks,
> Dewayne
>
> -----Original Message-----
> From: Sprinklerforum
> [mailto:[email protected]] On Behalf Of
> Jerry Van Kolken
> Sent: Thursday, April 09, 2015 6:49 PM
> To: [email protected]
> Subject: RE: NFPA 13 (07ed) apartment obstructions
>
> Looks like your you using the 4x rule . You should only need a single
> head at 36" away.
>
> Jerry Van Kolken
> Millennium Fire Protection
> (760) 722-2722
>
>
> -----Original Message-----
> From: Sprinklerforum
> [mailto:[email protected]]
> On Behalf Of Dewayne Martinez
> Sent: Thursday, April 09, 2015 10:16 AM
> To: [email protected]
> Subject: NFPA 13 (07ed) apartment obstructions
>
> I am using residential concealed pendant sprinklers in a NFPA 13
> apartment complex.  Many of the rooms have a surface mounted domed
> light which is about 12in in diameter and 5in deep at the center.  It
> seems to me that I must maintain at least 36in away from the edge of
> the light per figure
> 8.10.6.2.1.3 or install a sprinkler on both sides correct?
>
> Thanks,
>
> Dewayne
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.o
> rg
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.o
> rg
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.o
rg
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to