Thanks Travis. Perfect. That is what I remember. 

John

Sprinklers Save

> On Apr 13, 2015, at 9:36 AM, Tom Wellen <[email protected]> wrote:
> 
> Hence, that is the subject of Today’s Technical Update.  If you are not 
> getting Technical Updates as an AFSA member benefit, sign up.
> 
> 
> Small Room Design With Residential Sprinklers
> 
> "We are doing a NFPA 13 design with residential sprinklers.  Section 
> 11.3.1.3(2) allows calculating the area of coverage by the provisions of 
> either 8.5.2.1 or 8.6.2.1.2.  Does 8.6.2.1.2 apply to just pendent sprinklers 
> or can it be applied to sidewall sprinklers?"
> 
> We have reviewed the 2013 edition of NFPA 13 as the applicable standard.  Our 
> informal interpretation is that it applies to all types of residential 
> sprinklers.
> 
> It is understandable that there is some confusion here because Section 8.6 is 
> just for pendent sprinklers.  By Section 11.3.1.3 saying the provisions of 
> 8.6.2.1.2 apply means it is the methodology that is being discussed.  Keep in 
> mind that this section is referring to the half of the calculation where you 
> assign a density of 0.1 gpm/sq. ft. to the residential sprinkler.  You still 
> have to perform a calculation based on the listing of sprinkler that accounts 
> for the needs of the different sprinkler types.  This has been cleaned up for 
> the 2016 edition (see FR-261) that will say:
> 
> (3) In rooms or compartments 800 sq. ft. (74.3 sq. m) or less calculated 
> based on delivering a minimum of 0.1 gpm/sq. ft. (4.1 mm/min) over the room 
> or the compartment using the area of the room divided by the number of 
> sprinklers in the room.
> 
> This change emphasizes that it applies only to small rooms of no more than 
> 800 sq. ft. (when larger you must use 8.5.2.1) and that it applies to all 
> residential sprinklers.
> 
> 
> 
>> On Apr 13, 2015, at 8:27 AM, John Denhardt <[email protected]> 
>> wrote:
>> 
>> This was a lengthy discussion at a recent committee meeting. My position was 
>> it does not apply to sidewalls. Many of the committee said it did apply to 
>> sidewalls. For 2016, it should be clearer that it does apply to sidewalls.
>> 
>> Sprinklers Save
>> 
>>> On Apr 13, 2015, at 9:16 AM, Travis Mack <[email protected]> wrote:
>>> 
>>> That section appears to apply to residential sprinklers in general. The 
>>> portion in chapter 11 (2013 edition) points you to a specific section to 
>>> describe area per sprinkler for residential sprinklers.  I believe 2007 has 
>>> the same wording.
>>> 
>>> The section in chapter 8 that is referenced is for SSP/SSU. But chapter 11 
>>> specifically points you to the section about area. It is my understanding 
>>> that it applies to residential sidewall and pendent.
>>> 
>>> Will be interesting to see others opinion on this.
>>> 
>>> Travis Mack, SET
>>> MFP Design, LLC
>>> "Follow" us on Facebook: 
>>> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
>>> Send large files to MFP Design via:
>>> https://www.hightail.com/u/MFPDesign
>>> 
>>> Sent from my iPhone
>>> 
>>>> On Apr 13, 2015, at 6:00 AM, John Denhardt <[email protected]> 
>>>> wrote:
>>>> 
>>>> Agree, but in my opinion this rule did not apply to sidewalls. However, 
>>>> the 2016 edition might be adding sidewalls specifically.
>>>> 
>>>> Do not call about Stephs phoneSprinklers Save
>>>> 
>>>>> On Apr 13, 2015, at 8:44 AM, Travis Mack <[email protected]> wrote:
>>>>> 
>>>>> Dewayne:
>>>>> 
>>>>> I don't have the references in front of me but can get later today if you 
>>>>> need.
>>>>> 
>>>>> In NFPA 13, if you need the requirements for a small room, you can take 
>>>>> the area of the room divided by the number of sprinklers in the room to 
>>>>> get the area per sprinkler.
>>>>> 
>>>>> You then compare that to the listing of your sprinkler and use whichever 
>>>>> is greater.
>>>>> 
>>>>> For example, a 600 sq ft room with 4 residential sprinklers is 150 sq ft 
>>>>> per sprinkler. At 0.10 you have a minimum of 15 gpm. If sprinklers are 8' 
>>>>> off walls and no more than 16 ft apart, the listing for a 4.9k pendent is 
>>>>> 13 gpm so you use the 15 gpm from above.
>>>>> 
>>>>> If your sprinklers at 9' off walls, then you use 17 gpm because that is 
>>>>> the listing for 18' spacing of a 4.9k sprinkler.
>>>>> 
>>>>> I can find the exact references later today if you are unable to locate. 
>>>>> However, if you find where it says to do 4 sprinkler for residential 
>>>>> sprinklers, it is the next line or two down that points you to be the 
>>>>> room area method for standard spray that i mentioned above.
>>>>> 
>>>>> 
>>>>> Travis Mack, SET
>>>>> MFP Design, LLC
>>>>> "Follow" us on Facebook: 
>>>>> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
>>>>> Send large files to MFP Design via:
>>>>> https://www.hightail.com/u/MFPDesign
>>>>> 
>>>>> Sent from my iPhone
>>>>> 
>>>>>> On Apr 13, 2015, at 5:07 AM, Dewayne Martinez 
>>>>>> <[email protected]> wrote:
>>>>>> 
>>>>>> It would but I am using residential pendant sprinklers and the small room
>>>>>> rule only applies to standard throw sprinklers.
>>>>>> I guess that's the tradeoff I need to deal with for only wanting to calc 
>>>>>> 4
>>>>>> sprinklers and using extended coverage.
>>>>>> 
>>>>>> -----Original Message-----
>>>>>> From: Sprinklerforum
>>>>>> [mailto:[email protected]] On Behalf Of John
>>>>>> Denhardt
>>>>>> Sent: Monday, April 13, 2015 6:46 AM
>>>>>> To: <[email protected]>
>>>>>> Subject: Re: NFPA 13 (07ed) apartment obstructions
>>>>>> 
>>>>>> Does the small room apply?  If so, use .05 x small room rule or listing
>>>>>> whichever is larger.
>>>>>> 
>>>>>> Sprinklers Save
>>>>>> 
>>>>>>>> On Apr 13, 2015, at 7:38 AM, Dewayne Martinez
>>>>>>> <[email protected]> wrote:
>>>>>>> 
>>>>>>> Thanks for confirming Jerry.  The light is small and It just looks
>>>>>>> weird to have a head so far away from the center of the room where the
>>>>>>> light is located.  Of course when I have to offset the sprinkler so
>>>>>>> much it affects my calculations since it is a 13 application.  Glad
>>>>>>> the salesman bid it as if there were no lights present :) Thanks,
>>>>>>> Dewayne
>>>>>>> 
>>>>>>> -----Original Message-----
>>>>>>> From: Sprinklerforum
>>>>>>> [mailto:[email protected]] On Behalf Of
>>>>>>> Jerry Van Kolken
>>>>>>> Sent: Thursday, April 09, 2015 6:49 PM
>>>>>>> To: [email protected]
>>>>>>> Subject: RE: NFPA 13 (07ed) apartment obstructions
>>>>>>> 
>>>>>>> Looks like your you using the 4x rule . You should only need a single
>>>>>>> head at 36" away.
>>>>>>> 
>>>>>>> Jerry Van Kolken
>>>>>>> Millennium Fire Protection
>>>>>>> (760) 722-2722
>>>>>>> 
>>>>>>> 
>>>>>>> -----Original Message-----
>>>>>>> From: Sprinklerforum
>>>>>>> [mailto:[email protected]]
>>>>>>> On Behalf Of Dewayne Martinez
>>>>>>> Sent: Thursday, April 09, 2015 10:16 AM
>>>>>>> To: [email protected]
>>>>>>> Subject: NFPA 13 (07ed) apartment obstructions
>>>>>>> 
>>>>>>> I am using residential concealed pendant sprinklers in a NFPA 13
>>>>>>> apartment complex.  Many of the rooms have a surface mounted domed
>>>>>>> light which is about 12in in diameter and 5in deep at the center.  It
>>>>>>> seems to me that I must maintain at least 36in away from the edge of
>>>>>>> the light per figure
>>>>>>> 8.10.6.2.1.3 or install a sprinkler on both sides correct?
>>>>>>> 
>>>>>>> Thanks,
>>>>>>> 
>>>>>>> Dewayne
>>>>>>> _______________________________________________
>>>>>>> Sprinklerforum mailing list
>>>>>>> [email protected]
>>>>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>>>>>>> er.o
>>>>>>> rg
>>>>>>> 
>>>>>>> _______________________________________________
>>>>>>> Sprinklerforum mailing list
>>>>>>> [email protected]
>>>>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>>>>>>> er.o
>>>>>>> rg
>>>>>>> _______________________________________________
>>>>>>> Sprinklerforum mailing list
>>>>>>> [email protected]
>>>>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>>>>>>> er.org
>>>>>> _______________________________________________
>>>>>> Sprinklerforum mailing list
>>>>>> [email protected]
>>>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.o
>>>>>> rg
>>>>>> _______________________________________________
>>>>>> Sprinklerforum mailing list
>>>>>> [email protected]
>>>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>>> _______________________________________________
>>>>> Sprinklerforum mailing list
>>>>> [email protected]
>>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to