Agree, but in my opinion this rule did not apply to sidewalls. However, the 
2016 edition might be adding sidewalls specifically. 

Do not call about Stephs phoneSprinklers Save

> On Apr 13, 2015, at 8:44 AM, Travis Mack <[email protected]> wrote:
> 
> Dewayne:
> 
> I don't have the references in front of me but can get later today if you 
> need. 
> 
> In NFPA 13, if you need the requirements for a small room, you can take the 
> area of the room divided by the number of sprinklers in the room to get the 
> area per sprinkler. 
> 
> You then compare that to the listing of your sprinkler and use whichever is 
> greater. 
> 
> For example, a 600 sq ft room with 4 residential sprinklers is 150 sq ft per 
> sprinkler. At 0.10 you have a minimum of 15 gpm. If sprinklers are 8' off 
> walls and no more than 16 ft apart, the listing for a 4.9k pendent is 13 gpm 
> so you use the 15 gpm from above. 
> 
> If your sprinklers at 9' off walls, then you use 17 gpm because that is the 
> listing for 18' spacing of a 4.9k sprinkler. 
> 
> I can find the exact references later today if you are unable to locate. 
> However, if you find where it says to do 4 sprinkler for residential 
> sprinklers, it is the next line or two down that points you to be the room 
> area method for standard spray that i mentioned above. 
> 
> 
> Travis Mack, SET
> MFP Design, LLC
> "Follow" us on Facebook: 
> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
> Send large files to MFP Design via:
> https://www.hightail.com/u/MFPDesign
> 
> Sent from my iPhone
> 
>> On Apr 13, 2015, at 5:07 AM, Dewayne Martinez 
>> <[email protected]> wrote:
>> 
>> It would but I am using residential pendant sprinklers and the small room
>> rule only applies to standard throw sprinklers.
>> I guess that's the tradeoff I need to deal with for only wanting to calc 4
>> sprinklers and using extended coverage.
>> 
>> -----Original Message-----
>> From: Sprinklerforum
>> [mailto:[email protected]] On Behalf Of John
>> Denhardt
>> Sent: Monday, April 13, 2015 6:46 AM
>> To: <[email protected]>
>> Subject: Re: NFPA 13 (07ed) apartment obstructions
>> 
>> Does the small room apply?  If so, use .05 x small room rule or listing
>> whichever is larger.
>> 
>> Sprinklers Save
>> 
>>>> On Apr 13, 2015, at 7:38 AM, Dewayne Martinez
>>> <[email protected]> wrote:
>>> 
>>> Thanks for confirming Jerry.  The light is small and It just looks
>>> weird to have a head so far away from the center of the room where the
>>> light is located.  Of course when I have to offset the sprinkler so
>>> much it affects my calculations since it is a 13 application.  Glad
>>> the salesman bid it as if there were no lights present :) Thanks,
>>> Dewayne
>>> 
>>> -----Original Message-----
>>> From: Sprinklerforum
>>> [mailto:[email protected]] On Behalf Of
>>> Jerry Van Kolken
>>> Sent: Thursday, April 09, 2015 6:49 PM
>>> To: [email protected]
>>> Subject: RE: NFPA 13 (07ed) apartment obstructions
>>> 
>>> Looks like your you using the 4x rule . You should only need a single
>>> head at 36" away.
>>> 
>>> Jerry Van Kolken
>>> Millennium Fire Protection
>>> (760) 722-2722
>>> 
>>> 
>>> -----Original Message-----
>>> From: Sprinklerforum
>>> [mailto:[email protected]]
>>> On Behalf Of Dewayne Martinez
>>> Sent: Thursday, April 09, 2015 10:16 AM
>>> To: [email protected]
>>> Subject: NFPA 13 (07ed) apartment obstructions
>>> 
>>> I am using residential concealed pendant sprinklers in a NFPA 13
>>> apartment complex.  Many of the rooms have a surface mounted domed
>>> light which is about 12in in diameter and 5in deep at the center.  It
>>> seems to me that I must maintain at least 36in away from the edge of
>>> the light per figure
>>> 8.10.6.2.1.3 or install a sprinkler on both sides correct?
>>> 
>>> Thanks,
>>> 
>>> Dewayne
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>>> er.o
>>> rg
>>> 
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>>> er.o
>>> rg
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>>> er.org
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.o
>> rg
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to