Check 13. It applies to residential pendants also when applying the .1 rule. 
Ignore my earlier.05 reference. Monday morning! 

I do not have a copy of 13 with me or I would give you a reference. 

More changes coming to 2016 to allow for sidewalls in small rooms - 
residential. 

Sprinklers Saves

> On Apr 13, 2015, at 7:59 AM, Dewayne Martinez 
> <[email protected]> wrote:
> 
> It would but I am using residential pendant sprinklers and the small room
> rule only applies to standard throw sprinklers.
> I guess that's the tradeoff I need to deal with for only wanting to calc 4
> sprinklers and using extended coverage.
> 
> -----Original Message-----
> From: Sprinklerforum
> [mailto:[email protected]] On Behalf Of John
> Denhardt
> Sent: Monday, April 13, 2015 6:46 AM
> To: <[email protected]>
> Subject: Re: NFPA 13 (07ed) apartment obstructions
> 
> Does the small room apply?  If so, use .05 x small room rule or listing
> whichever is larger.
> 
> Sprinklers Save
> 
>>> On Apr 13, 2015, at 7:38 AM, Dewayne Martinez
>> <[email protected]> wrote:
>> 
>> Thanks for confirming Jerry.  The light is small and It just looks
>> weird to have a head so far away from the center of the room where the
>> light is located.  Of course when I have to offset the sprinkler so
>> much it affects my calculations since it is a 13 application.  Glad
>> the salesman bid it as if there were no lights present :) Thanks,
>> Dewayne
>> 
>> -----Original Message-----
>> From: Sprinklerforum
>> [mailto:[email protected]] On Behalf Of
>> Jerry Van Kolken
>> Sent: Thursday, April 09, 2015 6:49 PM
>> To: [email protected]
>> Subject: RE: NFPA 13 (07ed) apartment obstructions
>> 
>> Looks like your you using the 4x rule . You should only need a single
>> head at 36" away.
>> 
>> Jerry Van Kolken
>> Millennium Fire Protection
>> (760) 722-2722
>> 
>> 
>> -----Original Message-----
>> From: Sprinklerforum
>> [mailto:[email protected]]
>> On Behalf Of Dewayne Martinez
>> Sent: Thursday, April 09, 2015 10:16 AM
>> To: [email protected]
>> Subject: NFPA 13 (07ed) apartment obstructions
>> 
>> I am using residential concealed pendant sprinklers in a NFPA 13
>> apartment complex.  Many of the rooms have a surface mounted domed
>> light which is about 12in in diameter and 5in deep at the center.  It
>> seems to me that I must maintain at least 36in away from the edge of
>> the light per figure
>> 8.10.6.2.1.3 or install a sprinkler on both sides correct?
>> 
>> Thanks,
>> 
>> Dewayne
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>> er.o
>> rg
>> 
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>> er.o
>> rg
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
>> er.org
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.o
> rg
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to