We've had cases in the past where the detection part of the PA system just got 
left off the table.  Someone assumed someone else would be doing it and it just 
never got done.  Then at the 11th hour this is discovered and the finger 
pointing begins. Then we've had where two parties were installing detection in 
spaces and the project ended up with unnecessary duplicity again due to lack of 
engineering coordination.

So to curb that, I spec the detection part of the PA systems in with the SPRK 
work, with the intention of it being the sole responsibility of the sprinkler 
contractor.  He can then self-perform if able or sub it out to the project 
FA/EL or whatever contractor as they wish.  But at the end of the day, the 
sprinkler guy is the go-to guy for anything related to the PA system.

This has worked much better in avoiding parts of the systems being forgotten or 
not connected.  Now when we don't have direct control over contracts and the GC 
allows for exceptions and doesn't pay attention to them, that's when things 
fall apart and get ugly.

Craig L. Prahl 
Fire Protection Group Lead/SME
CH2MHILL
Lockwood Greene
1500 International Drive
Spartanburg, SCĀ  29303
Direct - 864.599.4102
Fax - 864.599.8439
CH2MHILL Extension  74102
[email protected]



-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Rod DiBona
Sent: Tuesday, February 09, 2016 2:33 PM
To: [email protected]
Subject: RE: Preaction Systems Scope

Now that is a great idea Ron.... I think we have a winner.... Would really give 
us an out if they didn't take the voluntary alternate and would also likely 
have them asking all bidding contractors about their scope as you pointed out. 
thank you Ron!

-----Original Message-----
From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of rongreenman .
Sent: Tuesday, February 09, 2016 12:05 PM
To: [email protected]
Subject: Re: Preaction Systems Scope

You could have a base bid price excluding the electrics, with an "in bold"
extra for the inclusion electrics. That might get their attention and still let 
them compare apples to apples. I know I've done that and that started someone 
asking questions about just what the other bids included.

On Tue, Feb 9, 2016 at 11:00 AM, Rod DiBona <[email protected]> wrote:

> Thank you all for your help. That is what I thought but we were 
> starting to wonder if we were the only ones that seem to consistently 
> have this problem. We so clearly, in bold exclude it in detail and 
> then still end up with a fight at the end because the GC didn't buy it 
> out. We were considering just including all of it in all of our 
> preaction bids so they get a complete system and eliminate the hassle 
> but felt that this would make us less competitive if others weren't 
> doing the same. We will continue to exclude and see if we can't find a 
> better way to communicate that this is a likely scope gap unless it is 
> addressed at bid time.
>
> -----Original Message-----
> From: Sprinklerforum [mailto:
> [email protected]] On Behalf Of rongreenman .
> Sent: Tuesday, February 09, 2016 11:03 AM
> To: [email protected]
> Subject: Re: Preaction Systems Scope
>
> Here it is typically handled like Mike describes too. Everyone pretty 
> much knows the general's contracts guy will miss all the exclusion 
> clauses unless he's been bitten before. The object is to get the 
> building built with all systems working.
>
> On Tue, Feb 9, 2016 at 9:53 AM, Morey, Mike <[email protected]> wrote:
>
> > Typically we tried to let the project team work it out, but if they 
> > didn't or there wasn't a well defined project team to resolve these 
> > issues we'd typically take it out for numbers.  Usually we try and 
> > get the electrical/alarm bidders for the project to put a number on it.
> >
> > Mike Morey, CFPS, SET
> > Planner Scheduler/Designer
> > BMWC Constructors, Inc.
> > 1740 W. Michigan St, Indianapolis, IN 46222
> > O: 317.651.0596 | C: 317.586.8111
> > [email protected] | www.bmwc.com
> >
> > ________________________________________
> > From: Sprinklerforum
> > <[email protected]>
> > on behalf of Rod DiBona <[email protected]>
> > Sent: Tuesday, February 9, 2016 12:25 PM
> > To: [email protected]
> > Subject: Preaction Systems Scope
> >
> > I am wondering how most of you handle the detection and releasing 
> > systems for your preaction systems. We traditionally have excluded 
> > all electrical and alarm but find it very common that the fire alarm 
> > contractor was just smarts and parts and the electrician doesn't 
> > have it in his scope. Not very often have the ME and EE coordinated 
> > so that
> it is spelled out correctly.
> > So my question is do most of you include this scope and have an 
> > electrical subcontractor that runs the conduit, provides and 
> > installs the heats or detectors and programs the releasing panel or 
> > do you exclude? Thanks
> >
> >
> > Rod at Rapid Fire
> >
> >
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
> > kl er.org _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> >
> > http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprin
> > kl
> > er.org
> >
>
>
>
> --
> Ron Greenman
> Instructor
> Fire Protection Engineering Technology Bates Technical College
> 1101 So. Yakima Ave.
> Tacoma, WA 98405
>
> [email protected]
>
> http://www.bates.ctc.edu/fireprotection/
>
> 253.680.7346
> 253.576.9700 (cell)
>
> Member:
> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC
>
> They are happy men whose natures sort with their vocations. -Francis 
> Bacon, essayist, philosopher, and statesman (1561-1626)
>
> A problem well stated is a problem half solved. -Charles F. Kettering, 
> inventor and engineer (1876-1958) 
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkl
> er.org
>



--
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC, WFSC

They are happy men whose natures sort with their vocations. -Francis Bacon, 
essayist, philosopher, and statesman (1561-1626)

A problem well stated is a problem half solved. -Charles F. Kettering, inventor 
and engineer (1876-1958) _______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to