Still not sure what that is supposed  to represent or what you’re trying to 
calculate.


Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540
Fax - 864.920.7129
CH2MHILL Extension  77540
[email protected]


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Zachary Siegrist
Sent: Wednesday, May 18, 2016 3:42 PM
To: [email protected]
Subject: Re: Equation for sizing fire pump

Sorry, I am looking at the wrong equation.  That equation just ensures I have 
20 psi available at 159 percent.

On Wednesday, May 18, 2016, <[email protected]<mailto:[email protected]>> 
wrote:
What are you supplying with your pump?

I’m not seeing any correlation between a flow at 20 psi and sizing a pump.  
What flow are you talking about, a municipal flow rate or what?

If for sprinkler systems, you size the pump based on the characteristics of the 
water supply and the system demands.

There are ways to get an estimate on pump size but the final selection better 
be verified through hydraulic calculations.


Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540
Fax - 864.920.7129
CH2MHILL Extension  77540
[email protected]<javascript:_e(%7B%7D,'cvml','[email protected]');>

From: Sprinklerforum 
[mailto:[email protected]<javascript:_e(%7B%7D,'cvml','[email protected]');>]
 On Behalf Of Zachary Siegrist
Sent: Wednesday, May 18, 2016 3:23 PM
To: 
[email protected]<javascript:_e(%7B%7D,'cvml','[email protected]');>
Subject: Equation for sizing fire pump

Is there an equation to specify an appropriate pressure when sizing a fire 
pump? For example, when sizing gpm, I've always taken the GPM available at 20 
psi divided by 1.5 to give me the maximum GPM rating of the pump.  I'm 
inquiring to see if such a formula is available to size the pressure correctly. 
Can anyone help?

Zach Siegrist
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to