This is Brad not Zach David.
While we are waiting I just wanted to say I have been asking for 4 or 5
years here if someone will dig up an old certified pump curve and post the
nameplate psi and rpm. I am 99.44% (like Ivory soap) sure
I can tell you what the nameplate impeller diameter says.
Are you game?

Brad
On May 18, 2016 5:26 PM, "David Bitton" <[email protected]>
wrote:

> Hello Zach,
>
>
>
> In reviewing the various responses to this thread, I noticed that no one
> actually answered your original question.  Here's my attempt:
>
>
>
> The upper limit for the pump pressure rating can be estimated as follows:
>
>
>
> Nominal pressure = (175 psi - Y)/1.2
>
> Y = Maximum suction pressure (static pressure if the pump is fed by
> municipal mains)
>
>
>
> This formula is based on the following assumptions:
>
> 1.       The maximum pressure rating for the piping and system
> accessories is 175 psi.
>
> 2.       The pump shut-off pressure is 120% of the pressure at the rated
> flow (this can range from 100% to 140%, depending on the pump model).
>
>
>
> In addition, if the proposed pump will be driven by a diesel engine, the
> nominal pressure derived from the above expression may be divided by 1.21.
> The result would be the maximum pump pressure rating that would not require
> the installation of a relief valve.
>
>
>
> *David Bitton, ing.*
>
> *Les services de prévention des sinistres Quest inc.*
>
> *Quest Loss Control Services Inc.*
>
> 5100, rue de la Savane, bureau 200
>
> Montréal, QC H4P 1T8
>
> (514) 341-4545
>
> *www.questlosscontrol.com <http://www.questlosscontrol.com>*
>
>
>
>
>
> *From:* Sprinklerforum [mailto:
> [email protected]] *On Behalf Of *
> [email protected]
> *Sent:* Wednesday, May 18, 2016 5:15 PM
> *To:* [email protected]
> *Subject:* RE: Equation for sizing fire pump
>
>
>
> In some jurisdictions you have to install an automatic suction control
> valve to assure that you do not pull the municipal system lower than their
> prescribed pressure.
>
>
>
> Typically the 20 psi flow point is provided on hydrant flow tests most of
> the time by extrapolation.  If you have that data then determining if the
> pump will draw more than allowed is much simpler.
>
>
>
>
> *Craig L. Prahl*
> Fire Protection Group Lead/SME
> *CH2M*
> 200 Verdae Blvd.
> Greenville, SC  29607
> Direct - 864.920.7540
>
> Fax - 864.920.7129
>
> CH2MHILL Extension  77540
> [email protected]
>
>
>
> *From:* Sprinklerforum [mailto:
> [email protected]] *On Behalf Of *Zachary
> Siegrist
> *Sent:* Wednesday, May 18, 2016 5:07 PM
> *To:* [email protected]
> *Subject:* Re: Equation for sizing fire pump
>
>
>
> Yes, I was confusing sizing the pump with determining the max capacity for
> the pump.  Trying to avoid dropping below 20 psi which has been a problem
> in my jurisdiction. Thank you Brad for your substantive reply.
> On Wednesday, May 18, 2016, Brad Casterline <[email protected]>
> wrote:
>
> Please brush up on NFPA 20.
>
> bc
>
> On May 18, 2016 2:48 PM, "Travis Mack, SET" <[email protected]> wrote:
>
> I think he is trying to get at the max capacity of a pump so that the
> municipal water supply doesn't go below 20 psi.  So, if his factor comes to
> a max of 1200 and the system requires a 1500 gpm pump, then a tank is going
> to be required.  That is my assumption at least.
>
> Travis Mack, SET
>
> MFP Design, LLC
>
> 2508 E Lodgepole Drive
>
> Gilbert, AZ 85298
>
> 480-505-9271
>
> fax: 866-430-6107
>
> email:[email protected]
>
>
>
> http://www.mfpdesign.com
>
> https://www.facebook.com/pages/MFP-Design-LLC/92218417692
>
> Send large files to us via: https://www.hightail.com/u/MFPDesign
>
> LinkedIn: https://www.linkedin.com/in/travismack
>
> On 5/18/2016 12:46 PM, [email protected] wrote:
>
> Still not sure what that is supposed  to represent or what you’re trying
> to calculate.
>
>
>
>
> *Craig L. Prahl*
> Fire Protection Group Lead/SME
> *CH2M*
> 200 Verdae Blvd.
> Greenville, SC  29607
> Direct - 864.920.7540
>
> Fax - 864.920.7129
>
> CH2MHILL Extension  77540
> [email protected]
>
>
>
> *From:* Sprinklerforum [
> mailto:[email protected]] *On Behalf Of *Zachary
> Siegrist
> *Sent:* Wednesday, May 18, 2016 3:42 PM
> *To:* [email protected]
> *Subject:* Re: Equation for sizing fire pump
>
>
>
> Sorry, I am looking at the wrong equation.  That equation just ensures I
> have 20 psi available at 159 percent.
>
> On Wednesday, May 18, 2016, <[email protected]> wrote:
>
> What are you supplying with your pump?
>
>
>
> I’m not seeing any correlation between a flow at 20 psi and sizing a
> pump.  What flow are you talking about, a municipal flow rate or what?
>
>
>
> If for sprinkler systems, you size the pump based on the characteristics
> of the water supply and the system demands.
>
>
>
> There are ways to get an estimate on pump size but the final selection
> better be verified through hydraulic calculations.
>
>
>
>
> *Craig L. Prahl*
> Fire Protection Group Lead/SME
> *CH2M*
> 200 Verdae Blvd.
> Greenville, SC  29607
> Direct - 864.920.7540
>
> Fax - 864.920.7129
>
> CH2MHILL Extension  77540
> [email protected]
>
>
>
> *From:* Sprinklerforum [
> mailto:[email protected]
> <[email protected]>] *On Behalf Of *Zachary
> Siegrist
> *Sent:* Wednesday, May 18, 2016 3:23 PM
> *To:* [email protected]
> *Subject:* Equation for sizing fire pump
>
>
>
> Is there an equation to specify an appropriate pressure when sizing a fire
> pump? For example, when sizing gpm, I've always taken the GPM available at
> 20 psi divided by 1.5 to give me the maximum GPM rating of the pump.  I'm
> inquiring to see if such a formula is available to size the pressure
> correctly. Can anyone help?
>
>
>
> Zach Siegrist
>
>
>
> _______________________________________________
>
> Sprinklerforum mailing list
>
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>
>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to