Hello Zach,

 

In reviewing the various responses to this thread, I noticed that no one 
actually answered your original question.  Here's my attempt:

 

The upper limit for the pump pressure rating can be estimated as follows:

 

Nominal pressure = (175 psi - Y)/1.2

Y = Maximum suction pressure (static pressure if the pump is fed by municipal 
mains)

 

This formula is based on the following assumptions:

1.       The maximum pressure rating for the piping and system accessories is 
175 psi.

2.       The pump shut-off pressure is 120% of the pressure at the rated flow 
(this can range from 100% to 140%, depending on the pump model).

 

In addition, if the proposed pump will be driven by a diesel engine, the 
nominal pressure derived from the above expression may be divided by 1.21.  The 
result would be the maximum pump pressure rating that would not require the 
installation of a relief valve.

 

David Bitton, ing.

Les services de prévention des sinistres Quest inc.

Quest Loss Control Services Inc.

5100, rue de la Savane, bureau 200

Montréal, QC H4P 1T8

(514) 341-4545

www.questlosscontrol.com

 

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of [email protected]
Sent: Wednesday, May 18, 2016 5:15 PM
To: [email protected]
Subject: RE: Equation for sizing fire pump

 

In some jurisdictions you have to install an automatic suction control valve to 
assure that you do not pull the municipal system lower than their prescribed 
pressure.

 

Typically the 20 psi flow point is provided on hydrant flow tests most of the 
time by extrapolation.  If you have that data then determining if the pump will 
draw more than allowed is much simpler.

 


Craig L. Prahl 
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd. 
Greenville, SC  29607
Direct - 864.920.7540

Fax - 864.920.7129

CH2MHILL Extension  77540
[email protected]

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Zachary Siegrist
Sent: Wednesday, May 18, 2016 5:07 PM
To: [email protected]
Subject: Re: Equation for sizing fire pump

 

Yes, I was confusing sizing the pump with determining the max capacity for the 
pump.  Trying to avoid dropping below 20 psi which has been a problem in my 
jurisdiction. Thank you Brad for your substantive reply.
On Wednesday, May 18, 2016, Brad Casterline <[email protected]> wrote:

Please brush up on NFPA 20.

bc

On May 18, 2016 2:48 PM, "Travis Mack, SET" <[email protected] 
<javascript:_e(%7B%7D,'cvml','[email protected]');> > wrote:

I think he is trying to get at the max capacity of a pump so that the municipal 
water supply doesn't go below 20 psi.  So, if his factor comes to a max of 1200 
and the system requires a 1500 gpm pump, then a tank is going to be required.  
That is my assumption at least.

Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected] 
<javascript:_e(%7B%7D,'cvml','email:[email protected]');> 
 
http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign 
LinkedIn: https://www.linkedin.com/in/travismack

On 5/18/2016 12:46 PM, [email protected] 
<javascript:_e(%7B%7D,'cvml','[email protected]');>  wrote:

Still not sure what that is supposed  to represent or what you’re trying to 
calculate.  

 


Craig L. Prahl 
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd. 
Greenville, SC  29607
Direct - 864.920.7540

Fax - 864.920.7129

CH2MHILL Extension  77540
[email protected] <javascript:_e(%7B%7D,'cvml','[email protected]');> 

 

From: Sprinklerforum [mailto:[email protected] 
<javascript:_e(%7B%7D,'cvml','[email protected]');>
 ] On Behalf Of Zachary Siegrist
Sent: Wednesday, May 18, 2016 3:42 PM
To: [email protected] 
<javascript:_e(%7B%7D,'cvml','[email protected]');> 
Subject: Re: Equation for sizing fire pump

 

Sorry, I am looking at the wrong equation.  That equation just ensures I have 
20 psi available at 159 percent.  

On Wednesday, May 18, 2016, <[email protected] 
<javascript:_e(%7B%7D,'cvml','[email protected]');> > wrote:

What are you supplying with your pump?

 

I’m not seeing any correlation between a flow at 20 psi and sizing a pump.  
What flow are you talking about, a municipal flow rate or what?

 

If for sprinkler systems, you size the pump based on the characteristics of the 
water supply and the system demands.

 

There are ways to get an estimate on pump size but the final selection better 
be verified through hydraulic calculations.

 


Craig L. Prahl 
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd. 
Greenville, SC  29607
Direct - 864.920.7540

Fax - 864.920.7129

CH2MHILL Extension  77540
[email protected]

 

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Zachary Siegrist
Sent: Wednesday, May 18, 2016 3:23 PM
To: [email protected]
Subject: Equation for sizing fire pump

 

Is there an equation to specify an appropriate pressure when sizing a fire 
pump? For example, when sizing gpm, I've always taken the GPM available at 20 
psi divided by 1.5 to give me the maximum GPM rating of the pump.  I'm 
inquiring to see if such a formula is available to size the pressure correctly. 
Can anyone help?

 

Zach Siegrist

 

_______________________________________________
Sprinklerforum mailing list
[email protected] 
<javascript:_e(%7B%7D,'cvml','[email protected]');> 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

 


_______________________________________________
Sprinklerforum mailing list
[email protected] 
<javascript:_e(%7B%7D,'cvml','[email protected]');> 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to