I think he is trying to get at the max capacity of a pump so that the municipal water supply doesn't go below 20 psi. So, if his factor comes to a max of 1200 and the system requires a 1500 gpm pump, then a tank is going to be required. That is my assumption at least.

Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected]

http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign
LinkedIn: https://www.linkedin.com/in/travismack

On 5/18/2016 12:46 PM, [email protected] wrote:

Still not sure what that is supposed to represent or what you’re trying to calculate.


*Craig L. Prahl**
*Fire Protection Group Lead/SME
*CH2M*
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540

Fax - 864.920.7129

CH2MHILL Extension  77540
[email protected]

*From:*Sprinklerforum [mailto:[email protected]] *On Behalf Of *Zachary Siegrist
*Sent:* Wednesday, May 18, 2016 3:42 PM
*To:* [email protected]
*Subject:* Re: Equation for sizing fire pump

Sorry, I am looking at the wrong equation. That equation just ensures I have 20 psi available at 159 percent.

On Wednesday, May 18, 2016, <[email protected] <mailto:[email protected]>> wrote:

    What are you supplying with your pump?

    I’m not seeing any correlation between a flow at 20 psi and sizing
    a pump.  What flow are you talking about, a municipal flow rate or
    what?

    If for sprinkler systems, you size the pump based on the
    characteristics of the water supply and the system demands.

    There are ways to get an estimate on pump size but the final
    selection better be verified through hydraulic calculations.


    *Craig L. Prahl**
    *Fire Protection Group Lead/SME
    *CH2M*
    200 Verdae Blvd.
    Greenville, SC  29607
    Direct - 864.920.7540

    Fax - 864.920.7129

    CH2MHILL Extension  77540
    [email protected]
    <javascript:_e(%7B%7D,'cvml','[email protected]');>

    *From:*Sprinklerforum
    [mailto:[email protected]
    
<javascript:_e(%7B%7D,'cvml','[email protected]');>]
    *On Behalf Of *Zachary Siegrist
    *Sent:* Wednesday, May 18, 2016 3:23 PM
    *To:* [email protected]
    <javascript:_e(%7B%7D,'cvml','[email protected]');>
    *Subject:* Equation for sizing fire pump

    Is there an equation to specify an appropriate pressure when
    sizing a fire pump? For example, when sizing gpm, I've always
    taken the GPM available at 20 psi divided by 1.5 to give me the
    maximum GPM rating of the pump.  I'm inquiring to see if such a
    formula is available to size the pressure correctly. Can anyone help?

    Zach Siegrist



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to