Yes, I was confusing sizing the pump with determining the max capacity for
the pump.  Trying to avoid dropping below 20 psi which has been a problem
in my jurisdiction. Thank you Brad for your substantive reply.
On Wednesday, May 18, 2016, Brad Casterline <[email protected]> wrote:

> Please brush up on NFPA 20.
>
> bc
> On May 18, 2016 2:48 PM, "Travis Mack, SET" <[email protected]
> <javascript:_e(%7B%7D,'cvml','[email protected]');>> wrote:
>
>> I think he is trying to get at the max capacity of a pump so that the
>> municipal water supply doesn't go below 20 psi.  So, if his factor comes to
>> a max of 1200 and the system requires a 1500 gpm pump, then a tank is going
>> to be required.  That is my assumption at least.
>>
>> Travis Mack, SET
>> MFP Design, LLC
>> 2508 E Lodgepole Drive
>> Gilbert, AZ 85298480-505-9271
>> fax: 866-430-6107email:[email protected] 
>> <javascript:_e(%7B%7D,'cvml','email:[email protected]');>
>> http://www.mfpdesign.comhttps://www.facebook.com/pages/MFP-Design-LLC/92218417692
>> Send large files to us via: https://www.hightail.com/u/MFPDesign
>> LinkedIn: https://www.linkedin.com/in/travismack
>>
>> On 5/18/2016 12:46 PM, [email protected]
>> <javascript:_e(%7B%7D,'cvml','[email protected]');> wrote:
>>
>> Still not sure what that is supposed  to represent or what you’re trying
>> to calculate.
>>
>>
>>
>>
>> *Craig L. Prahl*
>> Fire Protection Group Lead/SME
>> *CH2M*
>> 200 Verdae Blvd.
>> Greenville, SC  29607
>> Direct - 864.920.7540
>>
>> Fax - 864.920.7129
>>
>> CH2MHILL Extension  77540
>> [email protected]
>> <javascript:_e(%7B%7D,'cvml','[email protected]');>
>>
>>
>>
>> *From:* Sprinklerforum [
>> mailto:[email protected]
>> <javascript:_e(%7B%7D,'cvml','[email protected]');>]
>> *On Behalf Of *Zachary Siegrist
>> *Sent:* Wednesday, May 18, 2016 3:42 PM
>> *To:* [email protected]
>> <javascript:_e(%7B%7D,'cvml','[email protected]');>
>> *Subject:* Re: Equation for sizing fire pump
>>
>>
>>
>> Sorry, I am looking at the wrong equation.  That equation just ensures I
>> have 20 psi available at 159 percent.
>>
>> On Wednesday, May 18, 2016, <[email protected]
>> <javascript:_e(%7B%7D,'cvml','[email protected]');>> wrote:
>>
>> What are you supplying with your pump?
>>
>>
>>
>> I’m not seeing any correlation between a flow at 20 psi and sizing a
>> pump.  What flow are you talking about, a municipal flow rate or what?
>>
>>
>>
>> If for sprinkler systems, you size the pump based on the characteristics
>> of the water supply and the system demands.
>>
>>
>>
>> There are ways to get an estimate on pump size but the final selection
>> better be verified through hydraulic calculations.
>>
>>
>>
>>
>> *Craig L. Prahl*
>> Fire Protection Group Lead/SME
>> *CH2M*
>> 200 Verdae Blvd.
>> Greenville, SC  29607
>> Direct - 864.920.7540
>>
>> Fax - 864.920.7129
>>
>> CH2MHILL Extension  77540
>> [email protected]
>>
>>
>>
>> *From:* Sprinklerforum [mailto:
>> [email protected]] *On Behalf Of *Zachary
>> Siegrist
>> *Sent:* Wednesday, May 18, 2016 3:23 PM
>> *To:* [email protected]
>> *Subject:* Equation for sizing fire pump
>>
>>
>>
>> Is there an equation to specify an appropriate pressure when sizing a
>> fire pump? For example, when sizing gpm, I've always taken the GPM
>> available at 20 psi divided by 1.5 to give me the maximum GPM rating of the
>> pump.  I'm inquiring to see if such a formula is available to size the
>> pressure correctly. Can anyone help?
>>
>>
>>
>> Zach Siegrist
>>
>>
>>
>> _______________________________________________
>> Sprinklerforum mailing [email protected] 
>> <javascript:_e(%7B%7D,'cvml','[email protected]');>http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>
>>
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> <javascript:_e(%7B%7D,'cvml','[email protected]');>
>>
>> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
>>
>>
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to