In some jurisdictions you have to install an automatic suction control valve to 
assure that you do not pull the municipal system lower than their prescribed 
pressure.

Typically the 20 psi flow point is provided on hydrant flow tests most of the 
time by extrapolation.  If you have that data then determining if the pump will 
draw more than allowed is much simpler.


Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540
Fax - 864.920.7129
CH2MHILL Extension  77540
[email protected]


From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Zachary Siegrist
Sent: Wednesday, May 18, 2016 5:07 PM
To: [email protected]
Subject: Re: Equation for sizing fire pump

Yes, I was confusing sizing the pump with determining the max capacity for the 
pump.  Trying to avoid dropping below 20 psi which has been a problem in my 
jurisdiction. Thank you Brad for your substantive reply.
On Wednesday, May 18, 2016, Brad Casterline 
<[email protected]<mailto:[email protected]>> wrote:

Please brush up on NFPA 20.

bc
On May 18, 2016 2:48 PM, "Travis Mack, SET" 
<[email protected]<javascript:_e(%7B%7D,'cvml','[email protected]');>> 
wrote:

I think he is trying to get at the max capacity of a pump so that the municipal 
water supply doesn't go below 20 psi.  So, if his factor comes to a max of 1200 
and the system requires a 1500 gpm pump, then a tank is going to be required.  
That is my assumption at least.

Travis Mack, SET

MFP Design, LLC

2508 E Lodgepole Drive

Gilbert, AZ 85298

480-505-9271<tel:480-505-9271>

fax: 866-430-6107<tel:866-430-6107>

email:[email protected]<javascript:_e(%7B%7D,'cvml','email:[email protected]');>



http://www.mfpdesign.com

https://www.facebook.com/pages/MFP-Design-LLC/92218417692

Send large files to us via: https://www.hightail.com/u/MFPDesign

LinkedIn: https://www.linkedin.com/in/travismack
On 5/18/2016 12:46 PM, 
[email protected]<javascript:_e(%7B%7D,'cvml','[email protected]');> 
wrote:
Still not sure what that is supposed  to represent or what you’re trying to 
calculate.


Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540<tel:864.920.7540>
Fax - 864.920.7129<tel:864.920.7129>
CH2MHILL Extension  77540
[email protected]<javascript:_e(%7B%7D,'cvml','[email protected]');>

From: Sprinklerforum 
[mailto:[email protected]<javascript:_e(%7B%7D,'cvml','[email protected]');>]
 On Behalf Of Zachary Siegrist
Sent: Wednesday, May 18, 2016 3:42 PM
To: 
[email protected]<javascript:_e(%7B%7D,'cvml','[email protected]');>
Subject: Re: Equation for sizing fire pump

Sorry, I am looking at the wrong equation.  That equation just ensures I have 
20 psi available at 159 percent.

On Wednesday, May 18, 2016, 
<[email protected]<javascript:_e(%7B%7D,'cvml','[email protected]');>> 
wrote:
What are you supplying with your pump?

I’m not seeing any correlation between a flow at 20 psi and sizing a pump.  
What flow are you talking about, a municipal flow rate or what?

If for sprinkler systems, you size the pump based on the characteristics of the 
water supply and the system demands.

There are ways to get an estimate on pump size but the final selection better 
be verified through hydraulic calculations.


Craig L. Prahl
Fire Protection Group Lead/SME
CH2M
200 Verdae Blvd.
Greenville, SC  29607
Direct - 864.920.7540<tel:864.920.7540>
Fax - 864.920.7129<tel:864.920.7129>
CH2MHILL Extension  77540
[email protected]<mailto:[email protected]>

From: Sprinklerforum [mailto:[email protected]] On 
Behalf Of Zachary Siegrist
Sent: Wednesday, May 18, 2016 3:23 PM
To: 
[email protected]<mailto:[email protected]>
Subject: Equation for sizing fire pump

Is there an equation to specify an appropriate pressure when sizing a fire 
pump? For example, when sizing gpm, I've always taken the GPM available at 20 
psi divided by 1.5 to give me the maximum GPM rating of the pump.  I'm 
inquiring to see if such a formula is available to size the pressure correctly. 
Can anyone help?

Zach Siegrist


_______________________________________________

Sprinklerforum mailing list

[email protected]<javascript:_e(%7B%7D,'cvml','[email protected]');>

http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


_______________________________________________
Sprinklerforum mailing list
[email protected]<javascript:_e(%7B%7D,'cvml','[email protected]');>
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to