Would you post the .fds file?

Allan Seidel
St. Louis, MO

> On Oct 11, 2016, at 10:12 AM, Brad Casterline <[email protected]> wrote:
> 
> A Quick Response sprinkler does not necessarily activate sooner than a 
> standard response sprinkler!
> For example, 155 SRs at 120 S.F. spacing might activate sooner than 155 QRs 
> at 225 S.F., be they regular pendent or concealers.
>  
> We are allowed to use design area reduction when the RTI is 50 (m-s)^2 or 
> less and it is listed as quick response, and three other conditions are met. 
> The RTI is the physical, non site specific property of the sprinkler, and the 
> 'listed as quick response' is the various spacings, ceiling heights, etc. 
> tested, with some kind of pass/fail citeria, which i assume includes a range 
> of minimum 'real' activation times.
>  
> I used 50 and 80 RTI for the QR and SR in the four activation times I showed. 
> In more detailed scenarios I have used 38 and 90 based on glass bulb 
> manufactures published data. I kind of winged the concealer cover plate, but 
> not totally-- I input specific heat, conductivity, and density for a dab of 
> solder, and made the plate disappear when the dab reached 135F.
>  
> I have been using FDS-SMV for 10 years. For sprinkler activation it is for 
> personal curiosity and to try to get a little more insight than I can get 
> from NFPA alone.
> I don't try to predict anything, I like looking at 'differences', based on 
> RTI, Temp rating, ceiling height, and spacing.
> Fascinating stuff, and I'm glad you brought the 'concealer twist' to my 
> activation curiosity Pete!  
>  
> thanks,
>  
> Brad
>  
>  
> From: Sprinklerforum [mailto:[email protected] 
> <mailto:[email protected]>] On Behalf Of 
> Larrimer, Peter A
> Sent: Tuesday, October 11, 2016 9:18 AM
> To: [email protected] 
> <mailto:[email protected]>
> Subject: RE: [EXTERNAL] RE: FM and Concealed Sprinklers
>  
> I can’t say I know what you are using for your model, nor how you model RTI’s 
> for concealed heads and cover plates, but it sort of begs the question.  Why 
> is there a NFPA 13 reduction in design areas for LH and OH when the QR 
> concealed head might be slower than a standard response; assuming your model 
> results are close to accurate regarding response times.  
>  
> Considering that most fires are controlled with the first one or two 
> sprinklers in LH and OH facility fires, maybe the QR vs SR isn’t a big deal 
> when it comes to required design areas?  
>  
> Thanks
> Pete
> _______________________________________________
> Sprinklerforum mailing list
> [email protected] 
> <mailto:[email protected]>
> http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org 
> <http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org>