We are in the final phases of designing a self-storage facility (Ord Haz,
Grp II) that has upright, quick response sprinklers with the deflectors at
least 18" above the top of the individual storage unit partitions. In some
cases where the units are 5'x5' or 5'x10' we have located the sprinklers
directly over the top of the low partition. Our design concept is that the
sprinkler will throw evenly to each side of the partition and cover the
space on either side. This prevents us from have to "stagger" the sprinklers
with arm-overs to prevent spacing closer than 6' apart. We have also
provided the manufacturer's sprinkler spray pattern information to support
our design concept. 

 

Now the local plan reviewer is telling us that he will not accept this
sprinkler arrangement and that each unit has to have sprinkler(s) over them.
This is the second project that we have done in this jurisdiction and we ran
into a similar issue with the first one that we solved with the sprinkler
over the partition arrangement. Now he will not accept this solution, but he
doesn't site any code or handbook reference that we are violating. Is our
design concept  contrary to the provisions of NFPA-13? A review of NFPA-13
only specifically deals with sprinkler spacing over low partitions in light
hazard occupancies, not OH II, so I have no code guidance. 

 

Comments would be greatly appreciated.

 

John Paulsen - SET

Crown Fire System Design

6282 Seeds Rd.

Grove City, OH 43123

P - 614-782-2438

F - 614-782-2374

C - 614-348-8206

 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to