Ouch! Kinda makes you want to see him holding the 2 ½” hose by himself with
the pumper cranked up huh?

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Travis Mack, SET
Sent: Saturday, April 8, 2017 5:47 AM
To: [email protected]
Subject: Re: Sprinklers over low partitions

 

Don't feel bad.  I still remember the time that I had an NFPA interpretation
to back me up on a problem with an AHJ.  He told me that the opinion of the
technical committee members do not carry any more weight than his own.  And
that they were wrong.  That whole thing led to a jurisdiction requiring all
combination standpipes to be 6" minimum, regardless if calculated to be 4"
or not.

Travis Mack, SET
MFP Design, LLC
2508 E Lodgepole Drive
Gilbert, AZ 85298
480-505-9271
fax: 866-430-6107
email:[email protected] <mailto:email:[email protected]> 
 
http://www.mfpdesign.com
https://www.facebook.com/pages/MFP-Design-LLC/92218417692
Send large files to us via: https://www.hightail.com/u/MFPDesign 
LinkedIn: https://www.linkedin.com/in/travismack

On 4/8/2017 2:43 AM, John Paulsen wrote:

Thanks John,

 

Normally that would be the approach I would take, but I despair of any hope
in being able to educate this particular individual. I’ve tried twice with
no success. Sometimes it helps to know I’m not the one who’s nuts! It’s
getting harder and harder to tell these days.

 

John P

Crown FSD

 

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of 321
Sent: Saturday, April 8, 2017 5:39 AM
To: [email protected]
<mailto:[email protected]> 
Subject: Re: Sprinklers over low partitions

 

John,

 

Unfortunately....you are dealing with an AHJ that is subjectively making a
decision based on his personal ideas relative to Fire Sprinkler spacing and
operation. Further...he doesn't realize that the low partitions have no
effect upon the Fire Sprinkler operation or discharge characteristics.

 

Your challenge is to educate this person as to the fact that the NFPA
Technical Committee takes all factors into account in developing the codes.
I would suggest using some of the data from NFPA  13 on obstructions to
educate this person as to how the discharge cone develops and that there is
no more likelihood of a fire developing in the center of a space than there
is along one of these low partitions.

 

Good luck!

 

 

 

 

John W. Farabee

VP Fire Sprinkler Division

Atlantic Realty and Building, LLC

Jupiter, Fl

561-707-5150

Florida License No.

FPC16-000106

 

 

On Saturday, April 8, 2017 5:14 AM, John Paulsen <[email protected]
<mailto:[email protected]> > wrote:

 

We are in the final phases of designing a self-storage facility (Ord Haz,
Grp II) that has upright, quick response sprinklers with the deflectors at
least 18” above the top of the individual storage unit partitions. In some
cases where the units are 5’x5’ or 5’x10’ we have located the sprinklers
directly over the top of the low partition. Our design concept is that the
sprinkler will throw evenly to each side of the partition and cover the
space on either side. This prevents us from have to “stagger” the sprinklers
with arm-overs to prevent spacing closer than 6’ apart. We have also
provided the manufacturer’s sprinkler spray pattern information to support
our design concept. 

 

Now the local plan reviewer is telling us that he will not accept this
sprinkler arrangement and that each unit has to have sprinkler(s) over them.
This is the second project that we have done in this jurisdiction and we ran
into a similar issue with the first one that we solved with the sprinkler
over the partition arrangement. Now he will not accept this solution, but he
doesn’t site any code or handbook reference that we are violating. Is our
design concept  contrary to the provisions of NFPA-13? A review of NFPA-13
only specifically deals with sprinkler spacing over low partitions in light
hazard occupancies, not OH II, so I have no code guidance. 

 

Comments would be greatly appreciated.

 

John Paulsen – SET

Crown Fire System Design

6282 Seeds Rd.

Grove City, OH 43123

P – 614-782-2438

F – 614-782-2374

C – 614-348-8206

 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
<mailto:[email protected]> 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org









_______________________________________________
Sprinklerforum mailing list
[email protected]
<mailto:[email protected]> 
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to