I would ask the owner of the project to help you acquire information about 
mini storage industry standard practices. The reason that the partitions are 
not full height is the same reason that hospital curtains have a drop with a 
between the track and the top of the panel - it's for fire sprinkler 
distribution! The design of this building and those partial height partitions 
is to allow the exact basis of design concept that you have undertaken for the 
fire sprinkler system.

The first mini storage units I worked on as a designer had full height walls. 
When you have 5 by 5, 5 by 10 and 10 by 10 cells that each have a sprinkler, 
you can literally end up with 40 sprinklers in the design area. After doing a 
couple projects with ESFR-like demands, we worked with a local storage company 
to drop the walls and use heavy duty mesh on top of the partitions for security 
between individual units. This is now the norm and I would not take no for an 
answer in this situation. Get the owner of the project to help you in any way 
that they can. If, as owners often do, they try to pawn this off as your 
problem, then I would hit them for the additive change order you're entitled to 
for extra sprinklers and larger pipe size. That will get their attention and 
likely lead to some support for your argument.



Steve


-------- Original message --------
From: John Paulsen <[email protected]>
Date: 4/8/17 5:14 AM (GMT-05:00)
To: [email protected]
Subject: Sprinklers over low partitions

We are in the final phases of designing a self-storage facility (Ord Haz, Grp 
II) that has upright, quick response sprinklers with the deflectors at least 
18” above the top of the individual storage unit partitions. In some cases 
where the units are 5’x5’ or 5’x10’ we have located the sprinklers directly 
over the top of the low partition. Our design concept is that the sprinkler 
will throw evenly to each side of the partition and cover the space on either 
side. This prevents us from have to “stagger” the sprinklers with arm-overs to 
prevent spacing closer than 6’ apart. We have also provided the manufacturer’s 
sprinkler spray pattern information to support our design concept.

Now the local plan reviewer is telling us that he will not accept this 
sprinkler arrangement and that each unit has to have sprinkler(s) over them. 
This is the second project that we have done in this jurisdiction and we ran 
into a similar issue with the first one that we solved with the sprinkler over 
the partition arrangement. Now he will not accept this solution, but he doesn’t 
site any code or handbook reference that we are violating. Is our design 
concept  contrary to the provisions of NFPA-13? A review of NFPA-13 only 
specifically deals with sprinkler spacing over low partitions in light hazard 
occupancies, not OH II, so I have no code guidance.

Comments would be greatly appreciated.

John Paulsen – SET
Crown Fire System Design
6282 Seeds Rd.
Grove City, OH 43123
P – 614-782-2438
F – 614-782-2374
C – 614-348-8206


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to