John,
Unfortunately....you are dealing with an AHJ that is subjectively making a 
decision based on his personal ideas relative to Fire Sprinkler spacing and 
operation. Further...he doesn't realize that the low partitions have no effect 
upon the Fire Sprinkler operation or discharge characteristics.
Your challenge is to educate this person as to the fact that the NFPA Technical 
Committee takes all factors into account in developing the codes. I would 
suggest using some of the data from NFPA  13 on obstructions to educate this 
person as to how the discharge cone develops and that there is no more 
likelihood of a fire developing in the center of a space than there is along 
one of these low partitions.
Good luck!
  
John W. FarabeeVP Fire Sprinkler DivisionAtlantic Realty and Building, 
LLCJupiter, Fl561-707-5150Florida License No.FPC16-000106
 

    On Saturday, April 8, 2017 5:14 AM, John Paulsen <[email protected]> wrote:
 

 <!--#yiv1723190551 _filtered #yiv1723190551 {font-family:"Cambria 
Math";panose-1:2 4 5 3 5 4 6 3 2 4;} _filtered #yiv1723190551 
{font-family:Calibri;panose-1:2 15 5 2 2 2 4 3 2 4;}#yiv1723190551 
#yiv1723190551 p.yiv1723190551MsoNormal, #yiv1723190551 
li.yiv1723190551MsoNormal, #yiv1723190551 div.yiv1723190551MsoNormal 
{margin:0in;margin-bottom:.0001pt;font-size:11.0pt;font-family:"Calibri", 
sans-serif;}#yiv1723190551 a:link, #yiv1723190551 
span.yiv1723190551MsoHyperlink 
{color:#0563C1;text-decoration:underline;}#yiv1723190551 a:visited, 
#yiv1723190551 span.yiv1723190551MsoHyperlinkFollowed 
{color:#954F72;text-decoration:underline;}#yiv1723190551 
span.yiv1723190551EmailStyle17 {font-family:"Calibri", 
sans-serif;color:windowtext;}#yiv1723190551 .yiv1723190551MsoChpDefault 
{font-family:"Calibri", sans-serif;} _filtered #yiv1723190551 {margin:1.0in 
1.0in 1.0in 1.0in;}#yiv1723190551 div.yiv1723190551WordSection1 {}-->We are in 
the final phases of designing a self-storage facility (Ord Haz, Grp II) that 
has upright, quick response sprinklers with the deflectors at least 18” above 
the top of the individual storage unit partitions. In some cases where the 
units are 5’x5’ or 5’x10’ we have located the sprinklers directly over the top 
of the low partition. Our design concept is that the sprinkler will throw 
evenly to each side of the partition and cover the space on either side. This 
prevents us from have to “stagger” the sprinklers with arm-overs to prevent 
spacing closer than 6’ apart. We have also provided the manufacturer’s 
sprinkler spray pattern information to support our design concept.   Now the 
local plan reviewer is telling us that he will not accept this sprinkler 
arrangement and that each unit has to have sprinkler(s) over them. This is the 
second project that we have done in this jurisdiction and we ran into a similar 
issue with the first one that we solved with the sprinkler over the partition 
arrangement. Now he will not accept this solution, but he doesn’t site any code 
or handbook reference that we are violating. Is our design concept  contrary to 
the provisions of NFPA-13? A review of NFPA-13 only specifically deals with 
sprinkler spacing over low partitions in light hazard occupancies, not OH II, 
so I have no code guidance.   Comments would be greatly appreciated.  John 
Paulsen – SETCrown Fire System Design6282 Seeds Rd.Grove City, OH 43123P – 
614-782-2438F – 614-782-2374C – 614-348-8206    
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org


   
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to