Most cases it's only one or two lines in a small room. Usually it's just easier 
to run the length of the pipe till it exits room.  If there is a drip then the 
water is displaced completely out of the area.




Sent from my Verizon, Samsung Galaxy smartphone



Mark Phillips
Vice President of Fire Protection, Kirlin Carolinas, LLC
t: 919-526-1584
mphill...@jjkllc.com | http://www.kirlingroup.com
Raleigh, NC 27617
-------- Original message --------
From: Bob <b...@firebyknight.com>
Date: 2/2/18 6:23 PM (GMT-05:00)
To: sprinklerforum@lists.firesprinkler.org
Subject: RE: Shield for electrical equipment

Mark,
When installing this, does it need to run the entire length of the pipe or just 
where the pipe passes over the electrical equipment?

Thank you,

Bob Knight, CET III
208-318-3057

From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Phillips, Mark
Sent: Friday, February 02, 2018 2:33 PM
To: sprinklerforum@lists.firesprinkler.org
Subject: Re: Shield for electrical equipment

Are we maybe describing drip pans under pipe in electrical room?
Military jobs like this in their specs

It's usually sheet metal bent into a u shape a inch or so wider than pipe. Hung 
separately but touching bottom of pipe.
No obstruction
Unless I am misunderstanding


Sent from my Verizon, Samsung Galaxy smartphone


[https://signatures.kirlingroup.com/kirlinlogo.png]

Mark



Phillips


Vice President of Fire Protection

,

Kirlin Carolinas, LLC



t: 919-526-1584<tel:919-526-1584>


mphill...@jjkllc.com<mailto:mphill...@jjkllc.com>

 |

http://www.kirlingroup.com<http://www.jjkllc.com/>


Raleigh

,

NC



27617



[https://signatures.kirlingroup.com/twitter.png]<https://twitter.com/KirlinGroup>


[https://signatures.kirlingroup.com/facebook.png]<https://www.facebook.com/kirlinllc>


[https://signatures.kirlingroup.com/linkedin.png]<https://www.linkedin.com/company/133201/>





 -------- Original message --------
From: Bruce Verhei <bver...@comcast.net<mailto:bver...@comcast.net>>
Date: 2/2/18 4:23 PM (GMT-05:00)
To: 
sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>
Subject: Re: Shield for electrical equipment

Peter,

By 2019 ed. I assume you mean NEC?

Best.

Bruce Verhei

On Feb 2, 2018, at 11:20, Matthew J Willis 
<ma...@rapidfireinc.com<mailto:ma...@rapidfireinc.com>> wrote:
Or.., what if it's the panel on fire??

Sent from my Verizon 4G LTE Droid
On Feb 2, 2018 12:05 PM, Michael Goodis 
<m...@keyfps.com<mailto:m...@keyfps.com>> wrote:
I have to agree with Matt here.  If it is with-in 18” below the sprinklers it 
is considered an obstruction, if it is just under the piping, it does not allow 
for the water pattern to properly form to cover the room as the sprinklers are 
designed.

Regards,

Michael Goodis
Salesman, Project Manager
IL#000635   NICET#135586
Key Fire Protection Enterprises LLC
3200 Mike Padgett HWY
Augusta, GA 30906
Office- (706)790-3473
Cell- (706) 220-8822
Fax: (706) 738-2119



From: Sprinklerforum [mailto:sprinklerforum-boun...@lists.firesprinkler.org] On 
Behalf Of Matthew J Willis
Sent: Friday, February 2, 2018 1:40 PM
To: Forum 
<sprinklerforum@lists.firesprinkler.org<mailto:sprinklerforum@lists.firesprinkler.org>>;
 b...@firebyknight.com<mailto:b...@firebyknight.com>
Subject: Re: Shield for electrical equipment

I still sleeve pipe because I disagree with the shield allowance. To me it is 
an obstruction
For your case, I would defer that to electrical folks as we do not know their 
requirements per se.
R
Matt

Sent from my Verizon 4G LTE Droid
On Feb 2, 2018 11:36 AM, Bob 
<b...@firebyknight.com<mailto:b...@firebyknight.com>> wrote:
Has anyone installed a hood/ shield for electrical equipment?  Can this be 
something as simple as a sheet metal pan that covers the width and depth?
Suggestions, pictures, or name calling would be appreciated.


Thank you,

Bob Knight, CET III
208-318-3057
[FBK-LOGO-SMALL]

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@lists.firesprinkler.org<mailto:Sprinklerforum@lists.firesprinkler.org>