Why are you wanting to shield a head located under a Skylight?
Unfortunately some HVAC ducts already have been installed and because of this a couple of sprinklers must be placed under the skylight to comply with the cover areas, I want to shield the sprinkler to avoid any damage to the sprinkler if the skylight melt in case of fire. De: Sprinklerforum [mailto:[email protected]] En nombre de [email protected] Enviado el: lunes, 13 de agosto de 2018 09:04 a. m. Para: [email protected] Asunto: RE: Baffle for fire sprinkler system If you want a shielded sprinkler head, use a listed Intermediate level sprinkler head. Why are you wanting to shield a head located under a Skylight? Regards, G. Tim Stone G. Tim Stone Consulting, LLC NICET Level III Engineering Technician Fire Protection Sprinkler Design and Consulting Services 117 Old Stage Rd. - Essex Jct., VT. 05452 CELL: (802) 373-0638 TEL: (802) 434-2968 <mailto:[email protected]> [email protected] From: Sprinklerforum < <mailto:[email protected]> [email protected]> On Behalf Of Luis Perea Sent: Monday, August 13, 2018 10:54 AM To: <mailto:[email protected]> [email protected] Subject: Baffle for fire sprinkler system Does anyone know if there is a standard size of baffles to protect sprinklers? Some sprinklers are located under the skylight but NFPA does not mention anything related to the baffle size. I´m currently using a galvanized steel 12” x 12” shield to protect the sprinkler. Do you have any Thoughts?