Why are you wanting to shield a head located under a Skylight?

 

Unfortunately some HVAC ducts already have been installed and because of this a 
couple of sprinklers must be placed under the skylight to comply with the cover 
areas, I want to shield the sprinkler to avoid any damage to the sprinkler if 
the skylight melt in case of fire.

 

De: Sprinklerforum [mailto:[email protected]] En 
nombre de [email protected]
Enviado el: lunes, 13 de agosto de 2018 09:04 a. m.
Para: [email protected]
Asunto: RE: Baffle for fire sprinkler system

 

If you want a shielded sprinkler head, use a listed Intermediate level 
sprinkler head.

Why are you wanting to shield a head located under a Skylight?

 

Regards,

G. Tim Stone

 

G. Tim Stone Consulting, LLC

NICET Level III Engineering Technician

Fire Protection Sprinkler Design

and Consulting Services

 

   117 Old Stage Rd. - Essex Jct., VT. 05452

CELL: (802) 373-0638   TEL: (802) 434-2968

              <mailto:[email protected]> [email protected]

 

 

 

 

From: Sprinklerforum < <mailto:[email protected]> 
[email protected]> On Behalf Of Luis Perea
Sent: Monday, August 13, 2018 10:54 AM
To:  <mailto:[email protected]> 
[email protected]
Subject: Baffle for fire sprinkler system

 

Does anyone know if there is a standard size of baffles to protect sprinklers?

 

Some sprinklers are located under the skylight but NFPA does not mention 
anything related to the baffle size. 

I´m currently using a galvanized steel 12” x 12” shield to protect the 
sprinkler.

Do you have any Thoughts?

 

 