NFPA 13 only says to install intermediate Temperature Sprinkler heads beneath
Skylights. It is not a requirement of 13 to shield the head.
Regards,
G. Tim Stone
G. Tim Stone Consulting, LLC
NICET Level III Engineering Technician
Fire Protection Sprinkler Design
and Consulting Services
117 Old Stage Rd. - Essex Jct., VT. 05452
CELL: (802) 373-0638 TEL: (802) 434-2968
<mailto:[email protected]> [email protected]
From: Sprinklerforum <[email protected]> On Behalf
Of Luis Perea
Sent: Monday, August 13, 2018 11:23 AM
To: [email protected]
Subject: RE: Baffle for fire sprinkler system
Why are you wanting to shield a head located under a Skylight?
Unfortunately some HVAC ducts already have been installed and because of this a
couple of sprinklers must be placed under the skylight to comply with the cover
areas, I want to shield the sprinkler to avoid any damage to the sprinkler if
the skylight melt in case of fire.
De: Sprinklerforum [mailto:[email protected]] En
nombre de [email protected] <mailto:[email protected]>
Enviado el: lunes, 13 de agosto de 2018 09:04 a. m.
Para: [email protected]
<mailto:[email protected]>
Asunto: RE: Baffle for fire sprinkler system
If you want a shielded sprinkler head, use a listed Intermediate level
sprinkler head.
Why are you wanting to shield a head located under a Skylight?
Regards,
G. Tim Stone
G. Tim Stone Consulting, LLC
NICET Level III Engineering Technician
Fire Protection Sprinkler Design
and Consulting Services
117 Old Stage Rd. - Essex Jct., VT. 05452
CELL: (802) 373-0638 TEL: (802) 434-2968
<mailto:[email protected]> [email protected]
From: Sprinklerforum < <mailto:[email protected]>
[email protected]> On Behalf Of Luis Perea
Sent: Monday, August 13, 2018 10:54 AM
To: <mailto:[email protected]>
[email protected]
Subject: Baffle for fire sprinkler system
Does anyone know if there is a standard size of baffles to protect sprinklers?
Some sprinklers are located under the skylight but NFPA does not mention
anything related to the baffle size.
I´m currently using a galvanized steel 12” x 12” shield to protect the
sprinkler.
Do you have any Thoughts?
_______________________________________________
Sprinklerforum mailing list