Is the skylight plastic?  Have you asked the architect?  Even if it is, it is 
VERY unlikely that the skylight would melt before sprinklers were activated.

Typically, these types of commercial skylights are sandwiched glass panels.



Craig Prahl | Jacobs | Group Lead – Fire Protection | 864.676.5252 | 
[email protected] | www.jacobs.com<http://www.jacobs.com/>

From: Sprinklerforum <[email protected]> On Behalf 
Of Luis Perea
Sent: Monday, August 13, 2018 11:23 AM
To: [email protected]
Subject: [EXTERNAL] RE: Baffle for fire sprinkler system

Why are you wanting to shield a head located under a Skylight?

Unfortunately some HVAC ducts already have been installed and because of this a 
couple of sprinklers must be placed under the skylight to comply with the cover 
areas, I want to shield the sprinkler to avoid any damage to the sprinkler if 
the skylight melt in case of fire.

De: Sprinklerforum [mailto:[email protected]] En 
nombre de [email protected]<mailto:[email protected]>
Enviado el: lunes, 13 de agosto de 2018 09:04 a. m.
Para: 
[email protected]<mailto:[email protected]>
Asunto: RE: Baffle for fire sprinkler system

If you want a shielded sprinkler head, use a listed Intermediate level 
sprinkler head.
Why are you wanting to shield a head located under a Skylight?

Regards,
G. Tim Stone

G. Tim Stone Consulting, LLC
NICET Level III Engineering Technician
Fire Protection Sprinkler Design
and Consulting Services

   117 Old Stage Rd. - Essex Jct., VT. 05452
CELL: (802) 373-0638   TEL: (802) 434-2968
             [email protected]<mailto:[email protected]>




From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 On Behalf Of Luis Perea
Sent: Monday, August 13, 2018 10:54 AM
To: 
[email protected]<mailto:[email protected]>
Subject: Baffle for fire sprinkler system

Does anyone know if there is a standard size of baffles to protect sprinklers?

Some sprinklers are located under the skylight but NFPA does not mention 
anything related to the baffle size.
I´m currently using a galvanized steel 12” x 12” shield to protect the 
sprinkler.
Do you have any Thoughts?


[cid:[email protected]]

________________________________________________________________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to