I suspect you are attempting to address the requirement regarding the allowed 
maximum distance below the ceiling.  IF it’s a true skylight (well true per 
NFPA 13’s definition), then you can ignore the skylight and measure the 
distance based on the plane of the ceiling (see 8.5.7.1.1). 

Roland

Roland Huggins, PE - Senior VP Engineering
American Fire Sprinkler Assn.    
Dallas, TX
http://www.firesprinkler.org <http://www.firesprinkler.org/>

Fire Sprinklers Saves Lives




> On Aug 13, 2018, at 7:53 AM, Luis Perea <[email protected]> wrote:
> 
> Does anyone know if there is a standard size of baffles to protect sprinklers?
>  
> Some sprinklers are located under the skylight but NFPA does not mention 
> anything related to the baffle size. 
> I´m currently using a galvanized steel 12” x 12” shield to protect the 
> sprinkler.
> Do you have any Thoughts?
>  