Will the skylight even deflect before an intermediate sprinkler activates? Much 
less melt?

Get Outlook for iOS<https://aka.ms/o0ukef>

________________________________
From: 32412522240n behalf of
Sent: Monday, August 13, 2018 9:24 AM
To: [email protected]
Subject: RE: Baffle for fire sprinkler system

Why are you wanting to shield a head located under a Skylight?

Unfortunately some HVAC ducts already have been installed and because of this a 
couple of sprinklers must be placed under the skylight to comply with the cover 
areas, I want to shield the sprinkler to avoid any damage to the sprinkler if 
the skylight melt in case of fire.

De: Sprinklerforum [mailto:[email protected]] En 
nombre de [email protected]
Enviado el: lunes, 13 de agosto de 2018 09:04 a. m.
Para: [email protected]
Asunto: RE: Baffle for fire sprinkler system

If you want a shielded sprinkler head, use a listed Intermediate level 
sprinkler head.
Why are you wanting to shield a head located under a Skylight?

Regards,
G. Tim Stone

G. Tim Stone Consulting, LLC
NICET Level III Engineering Technician
Fire Protection Sprinkler Design
and Consulting Services

   117 Old Stage Rd. - Essex Jct., VT. 05452
CELL: (802) 373-0638   TEL: (802) 434-2968
             [email protected]<mailto:[email protected]>




From: Sprinklerforum 
<[email protected]<mailto:[email protected]>>
 On Behalf Of Luis Perea
Sent: Monday, August 13, 2018 10:54 AM
To: 
[email protected]<mailto:[email protected]>
Subject: Baffle for fire sprinkler system

Does anyone know if there is a standard size of baffles to protect sprinklers?

Some sprinklers are located under the skylight but NFPA does not mention 
anything related to the baffle size.
I´m currently using a galvanized steel 12” x 12” shield to protect the 
sprinkler.
Do you have any Thoughts?