NFPA 13 requires sprinklers in closets housing mechanical equipment. Is it
still considered a closet if it does not have a door? There is just a
removable panel to access the HVAC unit. There would be no access to the
sprinkler at the top of the space. NFPA 13 also requires sprinklers in all
closets except hotels & motels. Does Annex D 1.1.6.1 overide this
requirement for clothes closets in apartment buildings?

 