I believe the square foot limitation was removed in 2016 when the chapter
when Chapter 13 was listed as miscellaneous and low piled storage.

Bruce Hermanson

TSFP Holdings, Inc.

 

  _____  

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Vince Sabolik via Sprinklerforum
Sent: Wednesday, January 29, 2020 12:18 PM
To: [email protected]
Cc: Vince Sabolik
Subject: Re: Misc. Storage

 

Aren't there square footage limitations as well?



On 1/29/2020 11:03 AM, Skyler Bilbo via Sprinklerforum wrote:

Take a look at section 16.2.1.2.  I believe in your case, the Misc. Storage
criteria does apply.  However, for Class IV commodities on racks 10-12 ft
tall, the criteria is EH1, per the Misc. Storage Table 13.2.1. 

 

I believe where the biggest confusion, and the importance of the definition
comes into play, is with plastic storage over 5 feet, but under 12 feet.
There is not equivalent language to 16.2.1.2 in the plastic storage
chapters...

 

 




Skyler Bilbo 

 
<https://docs.google.com/uc?export=download&id=1Ot_QzTy6mc49_wnkJ-aKoPIBtkiv
O1gI&revid=0B1MzybbUMAWgNWRUNW03MkcyNkh4c0d4VXZMS0ZuQ2cvVzlFPQ> 

1700 S. Raney Street

Effingham, IL 62401

217-819-6404 Direct

217-347-7315 Fax

 

[email protected]

www.wenteplumbing.com

 

 

On Wed, Jan 29, 2020 at 9:44 AM Brian Harris via Sprinklerforum
<[email protected]> wrote:

Just want to confirm per the definition of Misc. Storage (3.9.1.18 NFPA
2013) that just because something is stored less than 12' high doesn't
automatically make it misc. storage. Working on a project that is 42,000
sq.ft. and the owner is storing Class I-IV commodities on double row racks.
Says he was told as long as he doesn't exceed 12' high he only needs OH-2
protection at the ceiling.

 

Brian Harris, CET

BVS Systems Inc.

Design Manager

bvssystemsinc.com <http://bvssystemsinc.com/> 

Phone: 704.896.9989

Fax: 704.896.1935

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org






_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org





-- 



11351 Pearl Road /  Suite 101
Strongsville, Ohio 44136 
Phone 440 238-4800 Fax 440 238-4876 Cell 440 724-7601


Vince Sabolik 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to