I should have clarified that I meant the square foot limitation on
miscellaneous storage if chapters 14-17 of 2016 kick you back to chapter 13
and the space can be classified as "low piled storage". 

Bruce

 

  _____  

From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Rocci 3 Cetani via Sprinklerforum
Sent: Thursday, January 30, 2020 10:51 AM
To: [email protected]
Cc: Rocci 3 Cetani; Parsley Consulting
Subject: RE: Misc. Storage

 

This one is intriguing to me.. If chapter 13 designates it an OH2 shouldn't
a system be allowed to be @ 52,000 sqft regardless of rack storage?

 

Rocci Cetani III, CET

Senior Designer

Water-Based Fire Protections Systems Layout, Nicet Level III

 

Northern California Fire Protection Services Inc.

16840 Joleen Way Bldg. A

Morgan Hill, CA 93037

P-(408) 776-1580 EXT.111

F-(408) 776-1590

 

 

[email protected]

www.norcalfire.com <http://www.norcalfire.com/> 

 

CONFIDENTIALITY NOTICE: This message and any document accompanying it may
contain confidential information 

belonging to the sender. The information is intended only for the use of
individual or entity named above. If you are not the intended recipient, or
the employee or agent responsible to deliver this message to the intended
recipient, you are hereby notified that any disclosure, copying or taking of
any action in reliance on the contents of this information is strictly
prohibited. If you have received this transmission in error, please
immediately notify us by telephone to arrange for return of the documents.

 

From: Sprinklerforum <[email protected]> On
Behalf Of Parsley Consulting via Sprinklerforum
Sent: Thursday, January 30, 2020 7:46 AM
To: Bruce Hermanson via Sprinklerforum
<[email protected]>
Cc: Parsley Consulting <[email protected]>
Subject: Re: Misc. Storage

 

Not quite, Bruce.

>From the 2019 edition:


What Brian was asking about was rack storage, so I would believe item 5
would still apply, regardless of the storage height.

Ken Wagoner, SET
Parsley Consulting
350 West 9th Avenue, Suite 206
Escondido, California 92025
Phone 760-745-6181
Visit the website <http://www.parsleyconsulting.com/>  

On 01/30/2020 3:35 AM, Bruce Hermanson via Sprinklerforum wrote:

I believe the square foot limitation was removed in 2016 when the chapter
when Chapter 13 was listed as miscellaneous and low piled storage.

Bruce Hermanson

TSFP Holdings, Inc.

 


  _____  


From: Sprinklerforum [mailto:[email protected]]
On Behalf Of Vince Sabolik via Sprinklerforum
Sent: Wednesday, January 29, 2020 12:18 PM
To: [email protected]
Cc: Vince Sabolik
Subject: Re: Misc. Storage

 

Aren't there square footage limitations as well?



On 1/29/2020 11:03 AM, Skyler Bilbo via Sprinklerforum wrote:

Take a look at section 16.2.1.2.  I believe in your case, the Misc. Storage
criteria does apply.  However, for Class IV commodities on racks 10-12 ft
tall, the criteria is EH1, per the Misc. Storage Table 13.2.1. 

 

I believe where the biggest confusion, and the importance of the definition
comes into play, is with plastic storage over 5 feet, but under 12 feet.
There is not equivalent language to 16.2.1.2 in the plastic storage
chapters...

 

 




Skyler Bilbo 

 
<https://docs.google.com/uc?export=download&id=1Ot_QzTy6mc49_wnkJ-aKoPIBtkiv
O1gI&revid=0B1MzybbUMAWgNWRUNW03MkcyNkh4c0d4VXZMS0ZuQ2cvVzlFPQ> 

1700 S. Raney Street

Effingham, IL 62401

217-819-6404 Direct

217-347-7315 Fax

 

[email protected]

www.wenteplumbing.com

 

 

On Wed, Jan 29, 2020 at 9:44 AM Brian Harris via Sprinklerforum
<[email protected]> wrote:

Just want to confirm per the definition of Misc. Storage (3.9.1.18 NFPA
2013) that just because something is stored less than 12' high doesn't
automatically make it misc. storage. Working on a project that is 42,000
sq.ft. and the owner is storing Class I-IV commodities on double row racks.
Says he was told as long as he doesn't exceed 12' high he only needs OH-2
protection at the ceiling.

 

Brian Harris, CET

BVS Systems Inc.

Design Manager

bvssystemsinc.com <http://bvssystemsinc.com/> 

Phone: 704.896.9989

Fax: 704.896.1935

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org





_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org





-- 


11351 Pearl Road /  Suite 101
Strongsville, Ohio 44136 
Phone 440 238-4800 Fax 440 238-4876 Cell 440 724-7601


Vince Sabolik 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://lists.firesprinkler.org/listinfo.cgi/sprinklerforum-firesprinkler.org

Reply via email to