Early in my career. I designed this very way. Especially in churches.

Given the wording though Down along the slope, your spray pattern cannot comply.

Not sure if it was in then, or if I just didn’t know at the time…

So hard wording dictates the only position given a slope exceeding 2/12”

Just my read.

R/
Matt

Please rate our customer 
service<https://survey.medallia.com/?emailsignature&fc=3539&bg=Fire%20and%20Fabrication>

Matthew J. Willis, CWBSP, CET
Engineering Designer IV
FERGUSON FIRE DESIGN, LLC
A Wholly Owned Subsidiary of Ferguson Fire & Fabrication, LLC
401 N 5th Street
Suite 448
Wausau, WI 54403
C: 307-236-8249
[email protected]<mailto:[email protected]>
www.FergusonFire.com<http://www.fergusonfire.com/>

From: Tony Silva <[email protected]>
Sent: Saturday, April 1, 2023 11:03 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Sidewall sprinklers for sloped roofs

from NFPA 13, 2013

8.7.4.2<http://8.7.4.2> Deflector Orientation.
8.7.4.2.1 Deflectors of sprinklers shall be aligned parallel to
ceilings or roofs.
8.7.4.2.2 Sidewall sprinklers, where installed under a sloped
ceiling with a slope exceeding 2 in 12, shall be located at the
high point of the slope and positioned to discharge downward
along the slope.

This section has been in NFPA 13, for a long time and has continued onto the 
current edition. As per this section, there is only one option for locating 
sidewall sprinklers under a steeply sloped roof. At the peak. to discharge 
downward along the slope.

I have a situation where the sloped piping is along a wall with the floor area 
being covered with two sidewall sprinklers. The deflectors of both sprinklers 
are installed parallel with the roof slope, positioned to discharge across the 
slope.The uppermost sidewall is located within 3 feet of the peak. I have been 
told that this configuration is incorrect as it is not permitted in NFPA 13.

Although it is not covered in NFPA, this orientation of sidewall sprinklers is 
shown in the residential sprinkler installation guides of all major 
manufacturers. Further, complying with 8.7.4.2<http://8.7.4.2> is problematic 
if the roof slopes both ways with the peak at the high point.

Any thoughts / comments?